I have connected the metallic armour of a 1 .5mm SWA cable (about 50ft run) to the met on the main CU using a 10mm earth cable. Is this a bit of an overkill or should I use 6mm earth cable instead?

What calculation applies to determine the cross section of the earth cable in this case?

Cheers!
 
Do you mean via flying lead off a banjo connection?? If so, i wouldn't bother replacing what's already installed, but yes it's a bit of an over kill as you put it...lol!! To determine the CPC size required use the adiabatic equation....
 
I have connected the metallic armour of a 1 .5mm SWA cable (about 50ft run) to the met on the main CU using a 10mm earth cable. Is this a bit of an overkill or should I use 6mm earth cable instead?

What calculation applies to determine the cross section of the earth cable in this case?

Cheers!

If it is a copper 1.5mm² line then you need no more than a copper 1.5mm² cpc :)

However 543.1.1 takes over and if it is not part of a cable then min size is 2.5mm² if protected; and 4mm² if not protected. So yes a bit of overkill with the 10mm²;)
 
If it is a copper 1.5mm² line then you need no more than a copper 1.5mm² cpc :)

However 543.1.1 takes over and if it is not part of a cable then min size is 2.5mm² if protected; and 4mm² if not protected. So yes a bit of overkill with the 10mm²;)

Thanks for the input, pushrod.
 

Reply to Earthing metallic armour of SWA cable. in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
It's the same with any system, if you put poo in, you get poo out!
Replies
4
Views
2K
  • Question
Why would the RCD fail … yes it can happen but then it may not. Without it you have no protection on the TT System
Replies
36
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top