Just received in a couple of hundred 240V IP65 light fittings from a well-known manufucture (Clue: What did the lion have pulled from its paw?) and not one of the steel Gear trays are in contact (zero continuity) with the Earthing point of the fitting!

The shell of fittings are non-conductive polycarbonate, but in my mind the 'guts' of the fitting should be in contact with the Earth, be it a fly lead or an Earthing screw.
If on a lamp change the live has come out and is touching the tray, this tray will now be live (insulated from Earth as its mounted in the non-conductive body so the MCB will not trip) if someone touches the tray they will get shocked.

Am I over thinking this, or is this the way 4' lamps are now manufactured, or is this a duff batch I have?


Thanks
 
The tray is normally earthed via the cable connector being in direct contact with the tray at the earth terminal itself. Is there a tab fitted and it's just paint covered on the tray?
 
Just received in a couple of hundred 240V IP65 light fittings from a well-known manufucture (Clue: What did the lion have pulled from its paw?) and not one of the steel Gear trays are in contact (zero continuity) with the Earthing point of the fitting!

The shell of fittings are non-conductive polycarbonate, but in my mind the 'guts' of the fitting should be in contact with the Earth, be it a fly lead or an Earthing screw.
If on a lamp change the live has come out and is touching the tray, this tray will now be live (insulated from Earth as its mounted in the non-conductive body so the MCB will not trip) if someone touches the tray they will get shocked.

Am I over thinking this, or is this the way 4' lamps are now manufactured, or is this a duff batch I have?


Thanks

Teach them to isolate it in future before changing the lamps then won't it.

What Top quark is saying that the terminal block where the mains connect to, the earth terminal will be screwed to a tab which is stamped out on the geartray,
 
As above, most of the fittings I've put up have the centre terminal on the connector block fitted to a pressed out tab, one make (can't remember name) of emergency lighting had a separate earth flylead with a lucar connector that went onto the tab.
 

Reply to Earthing of a gear tray in a light fitting in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top