Hi guys, I've got 2 x 10mm/sq at cu. 1 of them is giving me a ze reading of 176 ohms and the other 1 won't test on my fluke mf 1653b it is a tt install but no sign of rod.

How do I tell wether I'm getting a reading thru the gas or water bond, no signs of bonding any where.

Thanks
 
first if there's no bonding to gas or water, tou won't get your Zeaffected by them. yhis needs further investigation, as in find the rod or fit a new one , then go from there. get the bonding installed etc.
 
Are you sure there is an earth?

Is the system definitely TT and not an alternative supply missing an earth connection?

Always useful in situations like this if you take a picture to upload, even phones will do in most cases:thumbsup

*** Edit - Just read the comment about no sign of any bonding anywhere *** ;)
 
Last edited by a moderator:
There is no MET, just 2 10mm/sq single earths disappearing into wall.

Why am I getting 100 odd ohms on the one 10mm and then when testing on the other 10mm my tester makes a funny noise and won't test......think it comes up with error code 4. Im testing both exactly the same.
 
Are you getting sound contact on all terminals? I had a similar situation the other day when testing for Zs on a shower and I was adamant that I had sound contact but I had a re-shuffle, unplugged leads and re-plugged gave the fused connectors a good push to ensure they were connected properly and I then obtained a satisfactory reading.
 
Are you getting sound contact on all terminals? I had a similar situation the other day when testing for Zs on a shower and I was adamant that I had sound contact but I had a re-shuffle, unplugged leads and re-plugged gave the fused connectors a good push to ensure they were connected properly and I then obtained a satisfactory reading.

Yeah checked all contacts etc
keeping in mind that this is a house that been renovated about a year ago (full rewire) no ring mains, spurs from many sockets, 2 socKets never worked. DIYer by the looks. Old board with no cover on it, so any thing possible here if you get my drift
 
is this a semi?....or a terrace?.....shared supply maybe....just because you have a cutout at the C/U for this house doesn`t mean owt.......could be that the supply comes from next doors cutout into yours and its THEIR earthing arrangements or extranious that your reading.....
 

Reply to Earthing question? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
790
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
811

Similar threads

  • Solved
There is an article about that here: https://www.cement.org/learn/concrete-technology/durability/corrosion-of-embedded-materials It states...
2
Replies
27
Views
2K
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
947

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top