SimpleSimon

Could anyone point me out to a reg that states an earthing fly lead for a metal back box can be opted out if fixed lugs are involved?

Simon
Sent from my GT-I9100 using Tapatalk
 
It's guidance only....where I have seen it cant recall...could be in the OSG or one of the GN's.
 
Guidance on this is vague at best.

Essentially it's your call as to wether 411.4.2 can be satisfied by the path created by the faceplate screws or not. Guidance suggests that where both lugs are adjustable, this would not be the case and an earth lead should then be fitted.

IMHO, a flylead should always be fitted.
 
Guidance on this is vague at best.

Essentially it's your call as to wether 411.4.2 can be satisfied by the path created by the faceplate screws or not. Guidance suggests that where both lugs are adjustable, this would not be the case and an earth lead should then be fitted.

IMHO, a flylead should always be fitted.


Agreed...but did have a job a while ago fitting flat plate sockets to a job where the original installer had used 25mm boxes...(lazy git)...Leaving off the flylead made a surprising difference to getting the sockets back.
 
The requirement is to earth exposed-conductive-parts.
You have to decide, whether it is the metal back box is an exposed-conductive-part, that requires earthing, and whether the fixed lug, screw, etc would provide sufficient conductivity to be considered as providing a connection to the CPC.
 
Thanks gents.
Question came from a EICR last night. I said a fly lead is needed but another spark said no need as its fixed lugs.
ive never heard this point and couldnt find it in the regs.
Like you Lenny i would rather have the fly lead, metal face plate on a metal shop floor gondala...better safe than sorry.

Sent from my GT-I9100 using Tapatalk
 
Well I would have said that would definitely warrant a fly lead as that metal face plate being attached to a metal gondala(??) is an exposed conductive part

What is a gondala ?
 
Well I would have said that would definitely warrant a fly lead as that metal face plate being attached to a metal gondala(??) is an exposed conductive part

What is a gondala ?

On shop floors the mobile display units

Sent from my GT-I9100 using Tapatalk
 
Obviously we are assuming a T&E wiring system here, there are however some instances where a flylead MUST be fitted I.e, where the containment system or cable sheathing is being utilised as the CPC, galv conduit or MICC for example.

543.2.7 refers.

Sent from my BlackBerry 9800 using Tapatalk
 
good point, lenny. missed that one.
 
GN1...

Where an accessory has an earthing terminal incorporated, the protective conductor should be connected at the earthing terminal. Accessories which have an earthing terminal incorporated, such as socket-outlets, normally have an earth strap connecting the earthing terminal to one or both of the fixing holes. Flush metal accessory boxes usually have at least one fixed lug (see Figure 7.8). The IET Wiring Regulations Policy Committee has agreed that such boxes may be earthed via the tight metal-to-metal contact of the fixing screw in the fixed lug. Consequently, unless both lugs are of the adjustable type, it is not necessary to connect the earthing terminal of the accessory to the earthing terminal in the associated flush metal accessory box by a separate protective conductor (i.e. an earthing tail).

However, as mentioned in a post above, it has to be a tight metal connection.
 
GN1...

Where an accessory has an earthing terminal incorporated, the protective conductor should be connected at the earthing terminal. Accessories which have an earthing terminal incorporated, such as socket-outlets, normally have an earth strap connecting the earthing terminal to one or both of the fixing holes. Flush metal accessory boxes usually have at least one fixed lug (see Figure 7.8). The IET Wiring Regulations Policy Committee has agreed that such boxes may be earthed via the tight metal-to-metal contact of the fixing screw in the fixed lug. Consequently, unless both lugs are of the adjustable type, it is not necessary to connect the earthing terminal of the accessory to the earthing terminal in the associated flush metal accessory box by a separate protective conductor (i.e. an earthing tail).

However, as mentioned in a post above, it has to be a tight metal connection.

Thanks for posting that.

For the life of me I couldn't remember where I'd read it. :o)

Too many publications out there these days!

Sent from my BlackBerry 9800 using Tapatalk
 

Reply to the thread, titled "Earthing Reg" which is posted in Electrical Wiring, Theories and Regulations on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Earthing Reg
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
12

Thread Tags

Advert

Thread statistics

Created
SimpleSimon,
Last reply from
Guest123,
Replies
12
Views
1,962

Advert

Back
Top