Danny Pross

Hi
I have come a situation of "upgraded" (16mm and 10mm) earthing and bonding being attached to the original (and much thinner) earth to the supply sheathing.
Apparently the electrician didn't want to interfere with the original earth clamp to the sheath - so connected the old (thin) earth wire to the upgraded ones.
His reasoning was that if the ZE is ok then there is no problem.

I see what he is saying - but it just seems odd to upgrade effectively only part of the earth path.

I would be interested in any comments or advice on this.

Thanks

D
 
As far as i'm aware, the earth bonding on the sheath is before the meter and as such ownership is that of the supplier. To upgrade this would leave yourself in a very bad position as if there was a problem, you would be at fault and liable. The only course of action can be to inform the supplier and ask to be upgraded, however if the existing Ze reading is good then the supplier may want to charge for the upgrade. Personally i would leave alone as the Ze is good.
 
You cannot interfere with suppliers equipment (anything before the meter).

Therefore, if the Ze is acceptable, and the suppliers Earth Conductor complies with adiabatic requirements, use an Earth Block to connect the consumers installation to this.

I always position my Earth Block right next to the Cut Out and supply cable. This way, the DNO can easily install a spring clamp onto their cable, and the earth braid will easily reach the earth block.

If the Ze is high, phone the DNO or inform in writing.

If the provided Earth Conductor does not comply with adiabatic requirements, tell the DNO by phone or letter that by your calculation their conductor will melt in the event of an earth fault.
 
Agree with the above but just to add that if the Ze is too high, then contact the DNO as it is their responsibility to maintain it.
 

Reply to Earthing - TNS Upgrading Existing in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
546
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
990
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
921

Similar threads

In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top