Hi,

I was doing a CU change today when I checked one of the circuits which was supplying a shed. It came off a non-RCD 32a BS60898 and ran internally in 4mm T&E into an adaptable box which connected into 4mm SWA to run outside, then the same at the shed end.

The shed end has an RCD protected 2 way CU.

My concern is about the earthing, as the internal cable only has a 2.5mm cpc supplying the earthing for the shed.

Should I run a separate earth cable from the adabtable box to the CU as earth end and allow the Armour on the SWA to carry the earth outside.

The SWA is a two core cable.

It is a TNCS system.
 
I presume that due to the installation methods of the 4mm T&E and the 4mm SWA that a 32A breaker is ok?
 
I thought 4mm T&E had a 1.5mm CPC ? Regardless of that though as long as the Zs is low enough it's fine. If the SWA part of the supply is relying on the armour for CPC and has been there a long time I'd check under the gland shroud at the supply end to make sure the armour isn't corroding - seen this many times.
 

Reply to Earthing to shed supply in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
369
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
933
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I'm assuming the cable will have to be cleated well to hold it in place anyway, as a stuffing gland ain't going to hold it tight like a SWA gland...
Replies
10
Views
710
I hate it when a shed is TTd, why can they not be extended from the tn system? popcorn ready
Replies
7
Views
676

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top