Hi,
I was doing a CU change today when I checked one of the circuits which was supplying a shed. It came off a non-RCD 32a BS60898 and ran internally in 4mm T&E into an adaptable box which connected into 4mm SWA to run outside, then the same at the shed end.
The shed end has an RCD protected 2 way CU.
My concern is about the earthing, as the internal cable only has a 2.5mm cpc supplying the earthing for the shed.
Should I run a separate earth cable from the adabtable box to the CU as earth end and allow the Armour on the SWA to carry the earth outside.
The SWA is a two core cable.
It is a TNCS system.
I was doing a CU change today when I checked one of the circuits which was supplying a shed. It came off a non-RCD 32a BS60898 and ran internally in 4mm T&E into an adaptable box which connected into 4mm SWA to run outside, then the same at the shed end.
The shed end has an RCD protected 2 way CU.
My concern is about the earthing, as the internal cable only has a 2.5mm cpc supplying the earthing for the shed.
Should I run a separate earth cable from the adabtable box to the CU as earth end and allow the Armour on the SWA to carry the earth outside.
The SWA is a two core cable.
It is a TNCS system.