Hi guys, just got home from a job today at a golf course and am puzzled by the earthing arrangement.
The building is fed via 3 overhead powerlines that go to a transformer on a wooden pole approximatly 15 metres fromwhere it enters the building.
The 3 phase incommers go through a large green metal box filled with tar and then into a current transformer before going into a 300a 3P main switch and then onto a large C.U which in turn feeds many other sub mains around the building.
I took a Ze reading and got 35.0 ohms so was convinced it was a TT system, however upon inspection I can see that there is a large earth wire coming from behind the transformer outside, clipped directly to the wooden pole and then goes into the ground. When I looked behind the green tar filled box inside, I see that there is a clamp with the main earth (25mm) wire approx 5inch long going to to the MET.
Has anyone come accross this before, I thought if the electricity board supplied the earth it should be under 1 ohm no the 35.0 ohms I am getting. I even did a few Zs readings at internal sockets which ranged from 35.2 to 35.7 the further away I got.
All bonding appears up to date with services been earthed directly into the MET.
Heeeelpp (please)
The building is fed via 3 overhead powerlines that go to a transformer on a wooden pole approximatly 15 metres fromwhere it enters the building.
The 3 phase incommers go through a large green metal box filled with tar and then into a current transformer before going into a 300a 3P main switch and then onto a large C.U which in turn feeds many other sub mains around the building.
I took a Ze reading and got 35.0 ohms so was convinced it was a TT system, however upon inspection I can see that there is a large earth wire coming from behind the transformer outside, clipped directly to the wooden pole and then goes into the ground. When I looked behind the green tar filled box inside, I see that there is a clamp with the main earth (25mm) wire approx 5inch long going to to the MET.
Has anyone come accross this before, I thought if the electricity board supplied the earth it should be under 1 ohm no the 35.0 ohms I am getting. I even did a few Zs readings at internal sockets which ranged from 35.2 to 35.7 the further away I got.
All bonding appears up to date with services been earthed directly into the MET.
Heeeelpp (please)