clear as mud, are they saying all exposed metal parts of a bathroom need connecting via a cable to the main earth bar somehow? lets assume RCD of correct type is used to meet the requrement to remove the need for suplementary earthing what extra earthing do you need????? and how is it done physically
Okay. For the relaxation of supplementary bonding to be permissible, certain criteria have to be met.
i.e. all ccts in the location (supplying the bathroom/shower room etc) must be 30mA RCD protected,
& meet disconnection times.
Also, any extraneous conductive parts of the location must be
effectively connected to the MET.
I`ve highlighted the operative word there.
It is not a requirement for this to be done directly - it can (& more often, will) be achieved indirectly via the extraneous part`s remote connection to the main bonding conductor(s) & hence to the MET.
This connection must be proven to be effective/adaquate - no greater than 50 mOhms.
If these three pre-requisites are achieved then no supplementary bonding between the extraneous & exposed conductive parts need be provided.
Hope that`s clear enough for you. It`s all there in the On-Site, p69.
Al