SparkyJoe

A 3 phase DB has been wired with 3 X 25mm lock nut and bush into steel trunking, The ballbag has taken earths in one, neutrals in another, and phase conductors in the 3rd.

As im missing this bit of technical information, Do you get eddy currents if you have 3 phases going in one hole, or just if you have one

Cheers
 
A 3 phase DB has been wired with 3 X 25mm lock nut and bush into steel trunking, The ballbag has taken earths in one, neutrals in another, and phase conductors in the 3rd.

As im missing this bit of technical information, Do you get eddy currents if you have 3 phases going in one hole, or just if you have one

Cheers
IF!, perfectly balanced no net current on the neutral (very unlikely though!), really need neutral, CPC and all phases in the one hole, to eliminate possibility.
 
IF!, perfectly balanced no net current on the neutral (very unlikely though!), really need neutral, CPC and all phases in the one hole, to eliminate possibility.
yep..

i came across one not long back..

old 3 phase panel loaded up with 3036s

several entrys used for the phases & neutral....

it wasn`t anything to do with my work there....but it still went into the comments on existing installation box martin...
 
i think Darkwood had one as well..just the other day...as he was posting about it in here....and that was the handywork of an NIC AC...

so their out there....these ballbags...as has been described already...
 
Good for you matey!

Only get eddy's with changing fields, so if all phases are perfectly balanced (for all time) then no change in field for the phase bunching ... could still get something on the neutral or earth though even then, so still dodgy practice!
 
Good for you matey!

Only get eddy's with changing fields, so if all phases are perfectly balanced (for all time) then no change in field for the phase bunching ... could still get something on the neutral or earth though even then, so still dodgy practice!
but like you says...its unlikely...

there were multiple single phase loads on that thing i saw....various I N ...

its dicheads thats doing it...

i suppose they think it looks `neat & tidy`...or summat like that...
 
but like you says...its unlikely...

there were multiple single phase loads on that thing i saw....various I N ...

its dicheads thats doing it...

i suppose they think it looks `neat & tidy`...or summat like that...
Yep only needs a phase to go and yer shafted, ain't always under your control when things go pear shaped. zzzz
 
slots between the entrys does it as well...

I had drilled holes first before thinking about eddy currents, it was never actually made live with them in separate holes, like I say i did resolve the problem using paxolin. Yeah it's ok, not bad, could be neater but far from the worst out there, I don't have a great deal of experience with three phase Nd hooking a new board up, but we all have to start somewhere.
 

Reply to Eddy currents in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
295
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
277
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
354

Similar threads

  • Question
Three phase or single phase it is not correct.
Replies
1
Views
550
  • Question
Yes that is correct
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

  • exceeding voltage drop
    The cable is way undersized. If the voltage drop is detrimental to the installation I would make...
  • TT advise
    OK My take on the precautions to implement when omitting an up front RCD on a TT system. Tails...
  • SIL vs ATEX
    Good morning all, I have a question for those who are CompEx and SIL aware - I have various Ex...
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top