bulby

Hi

if i attend a house with bs3036 fuses what will the protection be EEBADS or ADS?

If its a 30amp fuse its a 0.4 s disconnection time , is this correct?
I am wiring a spur onto an exsisting ring main, just trying to get my head round the minor works cert
 
The new terminology, do i still have to get a 0.4 s disconnect time from a 30a bs3036?
Yes for a TN system. In order to achieve this your measured Zs <= 0.9 Ohms (OSG, Appendix 2,Table 2A)
 
Last edited by a moderator:
What is the earthing system? If it is TT then Zs could be high, up to 1667 ohms is allowed though it should be as low as possible. If it is TT then a 30mA RCD should be fitted which compensates/allows the Zs to be higher than stated in the tables.
 
What does the 30A BS3036 feed?
1/ If its a socket radial or small ring you could down rate the fuse to 20A (Yellow).
2/ You could increase the R2 by cross bonding to other circuit cpcs.
3/ If it is a TT system then there will be, or should be, a RCCB/Main Isolator at the origin of the installation which will give you a large amount of Zs leaway.

The original system should be designed to EEBADS, but that will mean main and supplementary bonding is in place. ADS is basically the same but also allows the use of other methods of protection such as RCDs and RCMs
 
Last edited:
Please tell me you are not being serious

Perfectly serious.

Have you heard of cross bonding?

and it doesn't have to be just the cpcs to create parallel earth paths.

Why do you think it states on the BS951 clip 'Safety Electrical Connection. Do Not Remove' ?
 
So what happens when the circuit C.P.C gets removed/ disconnected when it is no longer needed? The whole circuit that was relying on it is compromised.

The only proper way to increase r2 is by putting a larger C.S.A cable in.
 
So what happens when the circuit C.P.C gets removed/ disconnected when it is no longer needed? The whole circuit that was relying on it is compromised.

The only proper way to increase r2 is by putting a larger C.S.A cable in.


or supplementary bonding to reduce zs
 
But that isn't a guarenteed earth connection. What if the incomers to those bonded surfaces are later changed to plastic?
 
So what happens when the circuit C.P.C gets removed/ disconnected when it is no longer needed? The whole circuit that was relying on it is compromised.

The only proper way to increase r2 is by putting a larger C.S.A cable in.

Firstly, Why would anybody remove a circuit cpc?

Secondly, If you are referring to another circuit being used as a parallel path which has then become redundant then I would expect this to be picked up by the sparks doing the alterations.

It is still good practice to link cpcs across different circuits particularly in bathrooms, and recognized by the IET, to ensure low touch voltages under fault conditions. RCDs can sometimes fail.
 
Because the general public don't understand what they are doing, say you connected you parallel earth to a single socket on its own circuit and "Fred" wanted it removing but said why should I get a spark to do it when I can do it my self, there goes your parallel earth path and your circuit is compromised.

Where in the regs does it state any of that? That may have been in the the 16th edition when you bonded virtually everything.

So you are admitting that things can go wrong like a RCD failure, unfortunately that is something we can not account for when installing them, other wise we wouldn't carry out testing as it would be pointless.
 

Reply to the thread, titled "Eebads or ads" which is posted in Electrical Wiring, Theories and Regulations on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Eebads or ads
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
16

Thread Tags

Advert

Thread statistics

Created
bulby,
Last reply from
Engineer54,
Replies
16
Views
5,444

Advert

Back
Top