Hi guys, i'm not into testing on a regular basis. When testing a new build, all dead test done first. Energise installation when everything !00% ok.
How do you guys take Zs readings on "live" radial circuits?. If carrying out an EICR on an existing installation how is the Zs obtained on "live" radial circuits? Appreciate your thoughts.
 
just connect MFT to socket/light/whatever. perform loop impedance test. readings should increase the further along the radial you go. if RCD protected circuit, use the lo setting. most MFTs will require 3 lead connections for lo setting.
 
If you feel it is unsafe to carry out a live test on a circuit you can do an R1 + R2 test and calculate the Zs, there are also various adapters on the market for plugging into light fittings to help with the testing
 
If you feel it is unsafe to carry out a live test on a circuit you can do an R1 + R2 test and calculate the Zs, there are also various adapters on the market for plugging into light fittings to help with the testing

as long as you don't have megger test leads. they no work with lightmates.
 
re Zs testing I as thinking on the lines of radial circuits like Imm/htrs. Showers Cooker circuits with no 13a skts. I have done Zs testing before on radial cicuit , but now been informed that it is against the law Electricity at Works Act 1989.
 
not against the law. EWAR states that live working should only be undertaken when absolutely necessary. live testing is not the same as live working. it is , however, acceptable to calculate Zs from Ze and R1+R2 if you feel it's safer to do it that way.
 
not against the law. EWAR states that live working should only be undertaken when absolutely necessary. live testing is not the same as live working. it is , however, acceptable to calculate Zs from Ze and R1+R2 if you feel it's safer to do it that way.

Thanks........I've just watched a NICEIC dvd re testing, so thought I'd ask the question. they are basically saying apart from the ring main, Zs to be worked as you said above.
 
As long as you have insulated test probes and have check the connections are sound during relevant dead testing, I can't see any danger in carrying out a Zs test at spur or light switch. But as mentioned a Calculated Zs is accetable on an EICR
 

Reply to Eic / eicr testing question in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
949
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
https://professional-electrician.com/technical/replacing-a-consumer-unit-in-a-dwelling-niceic/ All circuits should be tested
Replies
3
Views
1K
Duh!!! Just re-read Op's original post, it was converted to a RFC!
Replies
12
Views
696

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top