Eic | on ElectriciansForums

Eic

Discuss Eic in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

D

daser66

Hi
could someone please explain part 6 on the schedule of items inspected.
many thanks
 
EIC = Electrical Installation Certificate
for a New Installations .. Addition to an existing installation or alteration to an existing installation

Im not sure what you call Part 6 is .. and are you looking at the Schedule of Tests Results Page.

Bit like this
[ElectriciansForums.net] Eic
 
I could well be wrong with this Gutterball so more replies would be good. I would read part 6 of the schedule of Inspections as being other types of protection against Electric shock, therefore if you have ADS as in domestic situations then part 6 is not applicable to you.

However... they specifically mention shaver socket which is confusing!

I must say I like the fact they have now added the regulations next to each point in the schedule of Inspections (for new installations).
 
Thanks Gutterball

[ElectriciansForums.net] Eic

This is the hand out that my tutor gave me..sorry i cant edit it.. CHROME is being a FOUR X and i cant work my GIMP!

That would have been EXTREMELY useful a few months ago so I have given you a thankyou anyway Duane, but unfortunately for the last few weeks we have a different 'schedule of Inspections (for new Installations) to complete :D (see page 5)

View attachment BS_7671_2008_AMD3-2015_Model_Forms.pdf
 
i was told they were going to change it to be like that .. oh well but thanks for the Link for AMD3 Forms

do we have to move over to this form now, i just filled in a old one for a test i am spose to do for NICEIC
 
Last edited by a moderator:
6.0 LOCATION(S) CONTAINING A BATH OR SHOWER
6.1 Additional protection for all low voltage (LV) circuits by RCD not exceeding 30 mA (701.411.3.3)
6.2 Where used as a protective measure, requirements for SELV or PELV met (701.414.4.5)
6.3 Shaver sockets comply with BS EN 61558-2-5 formerly BS 3535 (701.512.3)
6.4 Presence of supplementary bonding conductors, unless not required by BS 7671:2008 (701.415.2)
6.5 Low voltage (e.g. 230 volt) socket-outlets sited at least 3 m from zone 1 (701.512.3)
6.6 Suitability of equipment for external influences for installed location in terms of IP rating (701.512.2)
6.7 Suitability of accessories and controlgear etc. for a particular zone (701.512.3)
6.8 Suitability of current-using equipment for particular position within the location (701.55)

7.0 OTHER PART 7 SPECIAL INSTALLATIONS OR LOCATIONS
7.1 List all other special installations or locations present, if any. (Record separately the results of particularinspections applied.)

http://www.electriciansforums.co.uk...83-eic-bs_7671_2008_amd3-2015_model_forms.pdf

Download it, Print it, Read it.. and Tatoo it on your Arm or Leg
 
6.0 LOCATION(S) CONTAINING A BATH OR SHOWER
6.1 Additional protection for all low voltage (LV) circuits by RCD not exceeding 30 mA (701.411.3.3)
6.2 Where used as a protective measure, requirements for SELV or PELV met (701.414.4.5)
6.3 Shaver sockets comply with BS EN 61558-2-5 formerly BS 3535 (701.512.3)
6.4 Presence of supplementary bonding conductors, unless not required by BS 7671:2008 (701.415.2)
6.5 Low voltage (e.g. 230 volt) socket-outlets sited at least 3 m from zone 1 (701.512.3)
6.6 Suitability of equipment for external influences for installed location in terms of IP rating (701.512.2)
6.7 Suitability of accessories and controlgear etc. for a particular zone (701.512.3)
6.8 Suitability of current-using equipment for particular position within the location (701.55)

7.0 OTHER PART 7 SPECIAL INSTALLATIONS OR LOCATIONS
7.1 List all other special installations or locations present, if any. (Record separately the results of particularinspections applied.)

http://www.electriciansforums.co.uk...83-eic-bs_7671_2008_amd3-2015_model_forms.pdf

Download it, Print it, Read it.. and Tatoo it on your Arm or Leg

Duane! Youve now gone off on a tangent! That is Part 6 on a schedule form for an EICR not an EIC (see page 5 of the link I sent you).

As said before, I read Item No. 6 of the schedule of Inspections (for new installations) as relating to your main form of basic and fault protection which is ADS, therefore this section is generally N/A in a domestic setting. It's a pity Mr D.Skelton isn't still writing as I think this is something he could have shed some light on.
 
Last edited:

Reply to Eic in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
951
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Thanks for the advice, I actually had no idea about the HMO licensing rules so have learnt a lot. Just did a search, its not licensed as an HMO...
Replies
5
Views
400
So, I’m more aiming for the domestic setting myself and I don’t plan on EICR straight away. I am almost certainly not aiming for the industrial...
Replies
3
Views
377

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top