A

aes2011

Doing an EICR on an office block which has 2xsingle phase main boards. Old MEM type boards with 3036 fuses. Now given that there are no RCDs at all for cables concealed in Walls, sockets used by ordinary persons and so on. Does this warrant a C3-improvement recommended?
 
I would C3 it for lack of RCD, C2 if any sockets for outside use etc.

However this would also depend on the installation method and is it a controlled/supervised building?
 
Circuits run in PVC t&e and building occupied 9-5.
There is no EM lighting in building and the fire alarm panel looks ancient and only has a sounder and call point. Does this get recorded on eicr observations sheet?There are 7 offices on this level of building.
 
You are assessing the installation against current standards. Therefore no RCD protection for general purpose socket outlets, irrespective of who is plugging stuff in, is a code 3, as is the use of 3036 fuses. It was safe when it was originally designed and constructed, and if no defects other than non compliance with current standards then all is well now, so no defects exist, but you are recommending improvement to both protection of the installation and the users, but improvement is not mandatory.Their hand will be forced as and when they have additional work done in the future.

your concerns with the E lights and alarms are as rightly pointed out, outside of your remit when inspecting and testing the fixed installation, but i agree it is worth a note, not on the EICR, but elsewhere such as on your invoice, and then you have covered your ---.

Cheers.....Howard
 
Last edited by a moderator:
That is not so.
The requirement is to provide RCD protection for socket-outlets that are used by ordinary persons and intended for general use.
If they are not for use by ordinary persons, there is no requirement for RCD protection.
If they are for use by ordinary persons, but not intended for general use, there is again no requirement for RCD protection.
There are two exceptions.
One for if the use by ordinary persons for general use is supervised by a skilled or instructed person.
The other is a bit of a joke.
 
Basically the offices are occupied by accounts staff. Sockets are used for p.c's, fax, printers etc. So assuming no staff are electrically qualified and that a cleaner can plug her Hoover into any socket outlet she likes, RCD protection would be recommended. Either situation it is still C3.
 
Basically the offices are occupied by accounts staff. Sockets are used for p.c's, fax, printers etc. So assuming no staff are electrically qualified and that a cleaner can plug her Hoover into any socket outlet she likes, RCD protection would be recommended. Either situation it is still C3.

correct, unless there any outside/ used to supply portable equipment outside, then you could maybe code 2 it with a view to fitting an RCD socket
 
Basically the offices are occupied by accounts staff. Sockets are used for p.c's, fax, printers etc. So assuming no staff are electrically qualified and that a cleaner can plug her Hoover into any socket outlet she likes, RCD protection would be recommended. Either situation it is still C3.
Unfortunately, BS7671 does not have a code for instances where statutory requirements are not complied with.
It is a statutory requirement that the staff and cleaners should be what BS7671 regards as either skilled or instructed, if they are to use the socket-outlets.
Regulation 16 of the EAWR:
Persons to be competent to prevent danger and injury16. No person shall be engaged in any work activity where technical knowledge or experience is necessary to prevent danger or, where appropriate, injury, unless he possesses such knowledge or experience, or is under such degree of supervision as may be appropriate having regard to the nature of the work.
By applying ay code, you are effectively accusing the company of breaking the law.
 
Last edited by a moderator:
Unfortunately, BS7671 does not have a code for instances where statutory requirements are not complied with.
It is a statutory requirement that the staff and cleaners should be what BS7671 regards as either skilled or instructed, if they are to use the socket-outlets.
Regulation 16 of the EAWR:
Persons to be competent to prevent danger and injury16. No person shall be engaged in any work activity where technical knowledge or experience is necessary to prevent danger or, where appropriate, injury, unless he possesses such knowledge or experience, or is under such degree of supervision as may be appropriate having regard to the nature of the work.
By applying ay code, you are effectively accusing the company of breaking the law.

I don't believe plugging items or Hoover's in this case into socket outlets is a work activity that requires technical knowledge...

Its a code 3, the sockets are for general use by ordinary persons.

Sent from my LT26i using Tapatalk 2
 
Like I said, if you apply a code C3, you are effectivly calling the client a criminal.
It's a statutory requirement under the health and safety at work act, for any empoyee to be provided with the training required to carry out their work duties in as safe a manner as reasonably practicable.
The EAWR just reinforces that requirement with a specific reference to electricity.
Either the worker is trained or supervised whilst carrying out their work duties, or the employer is breaking the law.
BS7671 does not provide a standard for when the law is not being complied with.
Probably because it is deemed that if someone is willing to break the law, then they are hardly likely to bother with some non-statutory Regulations.
 
Like I said, if you apply a code C3, you are effectivly calling the client a criminal.
It's a statutory requirement under the health and safety at work act, for any empoyee to be provided with the training required to carry out their work duties in as safe a manner as reasonably practicable.
The EAWR just reinforces that requirement with a specific reference to electricity.
Either the worker is trained or supervised whilst carrying out their work duties, or the employer is breaking the law.
BS7671 does not provide a standard for when the law is not being complied with.
Probably because it is deemed that if someone is willing to break the law, then they are hardly likely to bother with some non-statutory Regulations.

I believe they will have the training to carry out there work and duties in a safe manner as is reasonably practical which in my opnion doesn't include electrical training to which they would be classed as a skilled person within BS7671...

To me your argument ( I say that term loosely as I know this isn't an argument) is one of an electrician in court trying to riggle out of a situation by using the grey areas where the british standards or laws may overlap.

By complying with BS7671 you as such comply with the EAWR to which we all work too (hopefully) and within that they are classed as ordinary persons and it warrants a C3. It's just a recommendation after all. The circuit or persons using it would be safer with it protected by an RCD wouldn't they?...

Sent from my LT26i using Tapatalk 2
 

Reply to EICR and 3036 fuses in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
321
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
848
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
971

Similar threads

Hi Dave thanks for the info I revisited the premises to change a cooker switch and redone the test from the MET with MET disconnected from DB...
Replies
16
Views
1K
i notice you mention "fire rated" instead of "metallic" Are we talking about a metal consumer unit? I know its presumed... but just checking
Replies
4
Views
695

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top