EICR and outside lighting | on ElectriciansForums

Discuss EICR and outside lighting in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Jacko

-
Joined
May 10, 2017
Messages
57
Reaction score
14
Location
Wales
Hello,

How would you go about testing outside lights on an EICR if they are supplied off an outside socket?

The sockets are supplied off the downstairs ring main, inside there is a 13amp switched fuse spur, then a double pole isolator running outside to 3 x double outdoor sockets all run in SWA. There is a ‘Knightsbridge remote control lighting switch’ inside a weatherproof box plugged into one of the sockets and that supplies 5 x lights fitted on the wall.

All SWA glands are fitted correct supplying the sockets, hi tuff cable is used for supplying the lights, all adaptable boxes and light fittings are correctly IP rated.

The lights can be unplugged (if you remove a small decking board) so would they be included in the test?

Thanks.
 
test up to and including the sockets. anything plugged in is outside of your remit.
 
As outside lights can be a potential source of danger, I would include them in the EICR.
They fall under Part P in any case. Not notifiable works necessarily, but part P covers all work in dwellings. Even if wired via a plug and socket.
 
This is the same sort of question from an earlier “entire conservatory wired from a plug top”

I think,if it’s wired as a permanent installation, such as part of it in SWA, then it’s gets tested.... and if it’s a single or group of say, under unit lighting on a plug, then no... don’t test it.
 
As outside lights can be a potential source of danger, I would include them in the EICR.
They fall under Part P in any case. Not notifiable works necessarily, but part P covers all work in dwellings. Even if wired via a plug and socket.
How often would you suggest an EICR on external floodlighting ? With the increase risk of open to the elements should they not be Inspected more frequently
 
You can and should set the next inspection set upon what you find during Inspection.
If you was to find all glanded watertight boxes siliconed along top and sides with good quality fittings this would attract a longer inspection interval than cheap fittings that are not so well wired.also if there is any chance the public can touch these a (RCD) Residual Current Device is required.i make sure all outside equipment has rcd
 

Reply to EICR and outside lighting in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

As the cable itself has had the cpc cut off at both ends I would enter a C3 as it doesn't offer any protection within the cable if accidentally...
Replies
3
Views
303
Is it a retaining wall? If so I'm of the opinion penetrating damp is almost impossible to avoid. Make a channel underneath for runoff and slosh...
Replies
5
Views
660

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top