Doing one more of the flood of EICR today on a rented property before a tenant change, but ran into a slightly interesting case so would appreciate other people's views.

About 6.5 years ago I partially rewired the small kitchen at this property - and since the main fuseboard was a skeleton wylex cupboard job and a pain to replace, I added a small Garage CU with 80A RCD to supply the 32A MCB for the kitchen ring to comply with RCD requirements (The main fuseboard has a 100ma RCD).

Today during the EICR, the newer RCD tested perfectly using the megger, but the test button is non functional - doesn't seem to have any resistance behind it so I'm guessing has mechanically failed.

The issue then becomes what code this is noted on the EICR.

Common sense may say it's best to change it since it could be a sign of failure. However, it passed the tests with no problem and therefore functions correctly as an RCD.

A previous thread discussed a similar topic 6 years ago and most people agreed this should be a C2.

However, the ESC best practise guide states that C2 codes are for situations that aren't dangerous at the time, but "would become an immediate danger if a fault or other foreseeable event was to occur"

This is a TN-S system, and the circuit in question has a low Zs so the RCD is not required to meet tripping limits for the MCB - it is there for additional protection as required by Regs.

If this was an EICR on an older board the absence of an RCD would be no more than a C3, so it seems slightly overkill to list this as a C2 and therefore grade the whole EICR as "unsatisfactory"

My own view is somewhere around a C2.5 for cases like this, or perhaps a C2 but a "satisfactory" rating, both of which are not options based on the guidelines.

Given that we know exactly 0.05% of people press the test button, whether quarterly or bi-annually, and given that an inspection will occur after 5 years, does the non-functioning test button actually have an outcome on the "electrical safety" of the installation, which is what the EICR is for after all?

I have no idea how frequently the test buttons fail in comparison to the rest of the device, or whether one it is always indicative of a developing fault.

EICR aside, assuming that the RCD should be replaced, the further wrinkle is that it was a LAP branded board, RCD and MCB, which I believe are no longer produced, (At the time the customer wanted to save money so a LAP garage unit was the chepest option.) so replacnig just the RCD would either mean mixing and matching (which is itself usually a C3 in my book) or entirely replacing the unit.

How would other electricians deal with that part, given that it's long past supplier's warranty periods? Bite some of the cost themselves as a goodwill gesture? (Obviously not installing LAP brand goes without saying, but given MK and the current situation who knows which brands will be around in 6 years?

Final note - any one know who made LAP stuff - and whether it is still made under a different brand?
 
You're giving them too much credit Tel, Scousers will just use cardboard boxes ?
that's just the posh ones . most Scousers settle for a body bag and a sea burial (dumped in the Mersey on the ebb tide).
 
As a matter of interest in the above scenario how would you justify that. What would be the likely danger? The test button does not work what harm can result from that?
Well as it would have been tested an FI wouldn't be required.
A C1 is out of the question - unless their were other circumstances.
A C3 would in all honesty be forgotten about - "Improvement recommended" I couldn't live with that if the future failure led to a possible death.
So C2 it is, from then on its out of my hands and up to the person receiving the report to do something about it.
If it stuck once, it will more than likely stick again.
Everyone to their own.
 
whatever you do, do not bin the RCD with the non working test button, with 65 posts, it has achieved celebrity status and will get a guest invitation to Loose Women,then a knighthood for being absolutely useless.
 
Well as I said above, I had a sticking test button and the RCD did not work on test. Once I had manually operated it, it worked and has been checked since and still works. Maybe I should have replaced then? After all it was a bit old, Merlin Gerin.
just shows that it's important to test by pressing the --- on a regular basis. i still recommend shorter interlvals than 6 months. i have a feeling that the 6 month requirement came in as customers could synchronise it with resetting the clocks twice a year. another case of pandering to numpties above safety.
 
just shows that it's important to test by pressing the --- on a regular basis. i still recommend shorter interlvals than 6 months. i have a feeling that the 6 month requirement came in as customers could synchronise it with resetting the clocks twice a year. another case of pandering to numpties above safety.
Six monthly is a common recommendation around the world. As you suggest when the clocks change is the logical time to do this. Although if the so-called EU has its way then it's hard to know when to recommend. Not too sure why we had the quarterly recommendation in the past.
 
Not too sure why we had the quarterly recommendation in the past.
For outdoor ones with a dedicated RCD, or plug adaptors, it was always a case of "test before use" so you have high confidence it is still working.

So presumably it started with a debate on how long between testing for board-mounted RCDs to gave acceptable fault detection given the move from dedicated outdoor sockets/adaptors to the widespread use of them on all domestic socket circuits. I have seen some RCDs that say test monthly, but that is just not going to be done, and other say "test regularly" but don't always say what that means (to give wriggle room in court?).
 

Reply to EICR Code for working RCD with non-functioning test button in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
953
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I would C2 this, cable is not suitable for the environment its installed in, we would C2 a socket for equipment likely to be used outside , cable...
Replies
11
Views
957
  • Question
If they got a shock then something cannot have been isolated.
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top