i always used to code 3 plastic consumer units as not AMD3 compliant,just wondering now 18th what others do ,ignore or code ?
 
653.2 The Report shall include the following:
- details of those parts of the installation that have been inspected and tested
- any limitations of the inspection and testing
- any damage, deterioration, defects or dangerous conditions
- any non-compliance with the requirements of BS 7671 which may give rise to danger.

Problem with code C3s, is there is no requirement to either comment or apply them.
 
Until January a plastic consumer unit was perfectly OK. Just because the 18th now requires them to be made of metal does not immediately make existing installed plastic ones unsafe or even non-compliant. They were compliant when installed and therefore they do not need coding unless for some reason they are likely to represent a hazard.

If the logic of coding is applied then you would have to code every change since installation - which would be a nonsense.
 

Reply to eicr code now 18th edition in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
811
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

Ah my mistake - apologies. I have something more or less like this wylex unit and the flappy plastic cover has got a broken pin so won't stay one...
Replies
4
Views
256
  • Question
Personally, I would take a Ze measurement myself rather than rely on someone else's maybe drive by scrap of paper.
2 3
Replies
31
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top