Thank you everyone for your very detailed answers, it makes it much clearer

I did actually ask the NAPIT technical guy about this today and it was all news to him, he had never seen the table B7 before and told me if it complies on the final circuits page it should be fine

I wonder how many general electricians are even aware of this?

Last question, Does anyone have any data for MEM memshield 2, C type 6a &10a mcb's and whether they too would be compliant on a 1mm CPC?

So im assuming if its not compliant, on an EICR a C3 code would be due maybe even a C2 which could have significant ramifications if its not possible to swap it over to a B type MCB
Can you reference this "non compliance" in BS7671.
 
Thank you everyone for your very detailed answers, it makes it much clearer

I did actually ask the NAPIT technical guy about this today and it was all news to him, he had never seen the table B7 before and told me if it complies on the final circuits page it should be fine

I wonder how many general electricians are even aware of this?
I suspect very few...
Last question, Does anyone have any data for MEM memshield 2, C type 6a &10a mcb's and whether they too would be compliant on a 1mm CPC?

So im assuming if its not compliant, on an EICR a C3 code would be due maybe even a C2 which could have significant ramifications if its not possible to swap it over to a B type MCB
The data for the Eaton Memshield MCBs lacks detailed info on the I2t let-through, which is disappointing.

However, given the OSG lists 1.5/1.0 circuits as compliant in Table 7.1 for 6/10A MCBs of both B & C curve I doubt it is a significant risk in practice. Has the DB in question got a PFC near or above 3kA?

I suspect if it is down in the 1-2kA region then really nothing to worry about.
 
I suspect very few...

The data for the Eaton Memshield MCBs lacks detailed info on the I2t let-through, which is disappointing.

However, given the OSG lists 1.5/1.0 circuits as compliant in Table 7.1 for 6/10A MCBs of both B & C curve I doubt it is a significant risk in practice. Has the DB in question got a PFC near or above 3kA?

I suspect if it is down in the 1-2kA region then really nothing to worry about.
Ok bit of a storm in a teacup then
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
Essex
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
EICR code - type C breakers with undersized CPC
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
19

Advert

Thread statistics

Created
Welchyboy1,
Last reply from
pc1966,
Replies
19
Views
4,557

Advert

Back
Top