EICR coding opinion? | on ElectriciansForums
Discuss EICR coding opinion? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
C
craig1000
Bathroom light fitting ceiling rose b/c type in zone one
C2 or C3, RCBO protected, existing install designed to previous regs?
thoughts appreciated?
are you sure it's zone 1? that's directly abath/shower and below 2.25m. what's the height?
Yep it is defo zone one, low ceiling in a basement flat, rose spans the edge of the bath and is basically on the edge of Z1 or Z2, i am taking the worst case and calling Z1
Ceiling height from ffl is 2.20
C2 was my gut feeling so is what it shall be just wanted to confirm with it being RCBO protected and old design/install!
Cheers guys! ;-)
Reply to EICR coding opinion? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
I would C2 this, cable is not suitable for the environment its installed in, we would C2 a socket for equipment likely to be used outside , cable...
The actual listed observations seem easily resolvable, comfortably less than a day's work. The picture of the supply poses a few questions...