Sockets are a ring main 2x line 2x neutral and 2x cpc however the cpc is trunking as one leg and single as the other leg.
Now all the sockets are taken from the metal trunking in plastic conduit so at each socket outlet the is only one cpc not two as no path through the plastic conduit
theres something very wrong about this set up.
either youve incorrectly identified the cpc system or the design is a complete lash up.
if youre using metal containment for multiple circuit cpc , thats fine , so long as Zs complies for each individual circuit relying on the trunking for earthing then theres nothing to code.
But if thats how its to be done then i'd like to see totally connected
steel conduit drops to switches and sockets , not a mash up of steel and pvc , thats asking for trouble.
and if you want to use seperate cpc's for the rings , thats fine , but do it as a proper loop , 1 in , 1 out as you would with t&e , cant see how you can effectively use only 1 cpc and the trunking which is linear in its route.
seems "odd"