rattlehead85

I am compiling an EICR on a period style house with wiring dating back to mid 60's. The installation has a fuseboard with 3036 fuses protecting all circuits. The bathroom has neither RCD protection or evident supplementary bonding arrangements although there is a 10mm bond to the main water stopcock. The lighting circuit has a class 2 enclosed light fitting and pull switch + a 230v extractor outside zones. What recommendation code should be attributed to this C2 or C3?
 
I would say C2 dangerous in the case of a fault, since there is no RCD protection in a bathroom with no supplementary bonding.
However you could check continuity between metalwork in the bathroom and if <0.05 ohms consider supplementary bonding to be in place, in which case it would be C3 improvement recommended.
 
Class II means they would have no earth and therefore would be safer than class I with exposed metalwork.

However so long as they are suitable for the environment, especially as they are outside zones, then they would be fine in all cases; outside of zones general wiring rules apply (except for sockets <3m from bath).
They would also be OK (except the pull switch) in zones 1 and 2 so long as they had IP protection to IPX4 or IPX5 if water jets.

What is worrying you about these items?
 
No the items and zoning i'm fine with. It was really just the issue of the lack of bonding to the location and if a c3 departure would be more appropriate seeing as class 2 equipment was in place.
 
I see what you mean, you are thinking that if there is no possibility to touch anything "earthy" then a fault that causes something to become live would not be a problem.
This is approaching a non conducting location, I don't think BS7671 has that allowance for bathrooms because of the increased risk of shock. I probably agree if there is no metal in the bathroom the risk is reduced, however you would have to be able to justify this is you decide in your professional judgment that this is safe.

I would not like to take the risk of effectively classifying it as ignore, which is how C3 is viewed.
Then again it has probably been safely in use for years, just like most of the installations that are around now.
 
Thanks guys for your opinions. I will tend to agree with classifying it as a code 2 as there is no evidence of any 16th edition bonding present with clamps or earthing connections in or even close to the location.
 
To my mind, It should be code C2 for lack of bonding, and code C3 for lack of RCD protection.
These are separate conditions which should be reported on individually and not be lumped together.
 

Reply to EICR departure code for bathroom. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
323
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
851
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
973

Similar threads

I would C2 this, cable is not suitable for the environment its installed in, we would C2 a socket for equipment likely to be used outside , cable...
Replies
11
Views
956
I would add a price for an eicr. they are highly unlikely to put in writing that it must be satisfactory for the order to be placed.
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top