Hi Guys,

I am looking for a bit of advice.

I am a landlord of a 1st floor flat in a small purpose-built block built in the mid eighties I think.

I have just had an EICR and have been cited C2s on the following :--

5.11 Provision of additional protection by 30mA RCD (See Note), c) For Cables concealed in walls / partitions at a depth of less than 50mm
Observation: No rcd present - C2

What are the likely cables are they talking about here?

7 Current-using equipment
7.2 Equipment does not constitute a fire hazard
Observation: bare connector blocks connecting the en-suite down-lights and smoke detector (which is in the hallway not in the en-suite - c2)

What sort of connectors should be used if these constitute a fire hazard?

8 Locations containing a bath or shower
8.4 Presence of supplementary bonding conductors unless not required by BS7671:2018
Observation: not present with no rcd protection - C2

Can you enlighten me on this one?

Do these items sound like Legitimate C2's ??? Or is someone trying to get some work out of me? Because they have included a quote of ÂŁ718 to resolve the 'urgent issues'. There were a few C3's as will including no RCD but I was expecting that.

If these issues are just 'touting for work' should I report it? If so who do you suggest I report to?
 
5.11 - C3, not compliant with present regs but was when installed.

7.2 - More info required either C1 or C3. If exposed, live conductive surface is touchable then C1. If a shonky taped up joint in a chock block then C3.

8.4 - C2, agree.

C3 shouldn't be seen as "can ignore" just that it is not an immediate danger or likely to become dangerous under fault conditions.

The taped up joint is an easy fix using Wago connectors in a maintenance free enclosure or other such product.

The others can be resolved by better RCD coverage.

Might be worth getting a few quotes for a board swap.

Having said all that without carrying out the EICR myself there may be some nuance I'm missing.
 
Agree with Westwood item 1 it a code 3 all day long and code 2 for the others ÂŁ718 pounds sounds bit expensive though . Do you know what work they are doing for that?
 
Agree with Westwood item 1 it a code 3 all day long and code 2 for the others ÂŁ718 pounds sounds bit expensive though . Do you know what work they are doing for that?


No ... As I said in the OP

to resolve the 'urgent issues' ÂŁ718 so don't know if that included installation of RCD or not.
 
For that price I would request list of what jobs they are doing I would guess a new consumer unit loaded with rcbos and new down lights .

Thanks for your reply.

If it did include what you assume do you think that would be a competitive quote for central London?
 
No ... As I said in the OP

to resolve the 'urgent issues' ÂŁ718 so don't know if that included installation of RCD or not.
Tha price should be a consumer unit change which will resolve two of the issues and 15mins and ÂŁ5 should resolve the other.


They've done an EICR so the circuits should be good to take RCD/RCBOs.

How many circuits?

Board change will need LA notification.
 

Reply to EICR - Do these C2's Sound Legit? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
939
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Definitely, although most likely within the accessories. I've often found that once accessories are disconnected the cabling IR is fine. Sometimes...
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top