Your thoughts on this please, there's 19 GU10 downlights on one circuit, NOT fire rated and the loft above has been boarded as you can see in picture. Who ever boarded it put a black ring around where a light was beneath it.

Any thoughts on what Code to give this if any, seems a bit of a fire hazard to me
[ElectriciansForums.net] EICR & downlights
 
C2 if there's insufficient airspace around and above downlighters, lift a board and see if there's any signs of scorching. C3 if they have space enough to dissipate heat. recommend cutting holes in boards. i would also check the terminations at each fitting. seen some shockers.
 
Just standard GU10 64mm downlights, they all have reflectors in dont they, spreading the light at different angles.

Tel there is no scorching on the undersides of the loft boards. But there is the usual faint scorch marks on ceiling around each downlight that I see on most downlights, there is gaps between each loft board that could disperse heat, but I still don't see how this is still acceptable. Every scenario I think that requires fire rated downlights someone pops up and says "no that's fine to install non fire rated there"

So what diffetent scenarios can you give that require fire rated downlights

Cheers all
 
So what diffetent scenarios can you give that require fire rated downlights

Cheers all

When cutting a hole in a ceiling breeches a fire compartment that could allow the spread of fire from one compartment to another.
Your situation doesn't call for fire rated fittings due to the above.
 
I think there's always confusion over the fitting of 'fire rated' downlights-as GaryM says, breaching a fire compartment is when these fittings MUST be installed.
A conventional house is classed as 1 fire compartment due to the big hole between floors where the stairs go.

Any fitting must have adequate air space around it as per manufacturers instructions.
 
An example would be downlghts in a self contained ground floor flat. Seperate living accommodation ( compartment ) above. I only fit fire rated but that's just my preference.

Sent from my HTC One X using Tapatalk 2
 
Have a read of this - Spring 2007 Wiring Matters - Installing Downlighters Safely

http://electrical.------.org/wiring-matters/22/down-lighters.cfm?type=pdf
 
Here's an article I came across a while ago:

INSTALLING RECESSED LUMINAIRES IN CEILINGS by Bill Allan
THE IEE receives a number of enquiries from designers and installers and others regarding the application of Regulation 527-02-01 when installing recessed luminaries in ceilings in domestic premises. Regulation 527-02-01 is clear enough. It requires that where a wiring system passes through elements of building construction such as floors, walls, roofs, ceilings, partitions or cavity barriers, the openings remaining after passage of the wiring system shall be sealed according to the degree of fire resistance required of the element concerned (if any). The two words in brackets at the end of the Regulation, (if any), highlight the problem. Simply stated, the question is: if an electrician is installing one or more recessed downlighters in a location such as a domestic kitchen, for example, what degree of fire resistance is required? Is any degree of fire resistance required
This question has been highlighted by the introduction of Part P into the Building Regulations. This article will not deal with protection against thermal effects, for which reference should be made to Chapter 42 of BS 7671: 2001 and IEE Guidance Note 4, Protection Against Fire. Reference should always be made to Part B of the Building Regulations for fire safety requirements. For sound insulation requirements, reference should be made to Part E of the Building Regulations. It should be emphasised at the outset that this article is intended to provide guidance, which, it is hoped, will prove helpful; it is recommended that the local building control be consulted for advice.
Fire compartments Let’s begin with a brief review of some theory about fire safety. The spread of fire within a building is restricted by sub-dividing the building into compartments separated from one another by walls and/or floors of fire-resisting construction. There are two reasons for this:  To prevent the rapid spread of fire that could trap occupants of the building; and  To reduce the chance of fires becoming large on the basis that large fires are more dangerous not only to occupants and fire service personnel but to people in the vicinity of the building.
Dwellings Walls that separate semi-detached houses or terraced houses are constructed as fire compartment walls and the houses are considered as separate buildings. Where a domestic garage is attached to a house, (or forms an integral part of it), the garage should be separated from the rest of the house. In buildings containing flats or maisonettes, every floor is constructed as a fire compartment floor (unless it is within a maisonette, i.e. between one storey and another within one dwelling) and every wall that separates a flat or a maisonette from any other part of the building is constructed as a fire compartment wall. Otherwise, the walls and ceilings within detached, semi-detached and terraced houses are not constructed as fire compartment walls and ceilings.
Installing downlighters in ceilings that are not fire compartments Downlighters are commonly installed in locations such as kitchen ceilings, which are not fire compartment ceilings. But because they are not fire compartment ceilings does not mean that they don’t require some degree of fire resistance. The minimum fire resistance of a floor in a two-storey house, for example, is given in Appendix A of Approved Document B , ‘Fire Safety’, as 30 minutes (See Table A1). The idea is that, in a fire situation, the floor will not collapse for at least 30 minutes, enabling building occupants to leave safely. Downlighters are usually made of steel or aluminium and have a diameter of approximately 50mm (the holes themselves being about 60mm). Common sense suggests that cutting a number of holes in the plasterboard ceiling of a timber joisted floor may compromise its fire resistance capability. One measure to help the situation is to keep the number of downlighters in any one area to a minimum and to space them as far apart as possible. Solutions proposed to restore the integrity of the ceiling’s fire resistance include building a plasterboard box around luminaires or installing commercially available ‘fire hoods’. But is it necessary to restore the fire resistance capability of ceilings?
The TTL tests In 1996, the DoE and TRADA commissioned TRADA Technology Limited (TTL), a member of the TTL Chiltern group of companies, to test the effect of recessed downlighters (with no boxing in or fire hoods) on the fire resistance of plasterboard ceilings with conventional rectangular joists. TTL has been involved in fire research and testing for many years and is the UK’s leading authority on the fire protection of timber. During 1994/95, TTL carried out the tests. The results of the tests were published in the July 1996 edition of Building Control magazine. These results were, perhaps, surprising in that they confirmed that downlighters, even without being boxed in and with no fire hoods, in plasterboard ceilings have little significant effect on fire resistance ratings up to 30 minutes. It must be inferred from these tests therefore, that, at least with plasterboard ceilings with conventional rectangular joists, it is not necessary to ‘box in’ luminaries or to use fire hoods for the purpose of restoring the fire resistance capability of ceilings which are not of fire compartment construction.
Downlighters in ceilings under roof spaces However, in situations where downlighters are installed in ceilings under roof spaces, where debris or thermal insulation may accumulate on top of the luminaire, a case could be made for building a plasterboard or metal box around the luminaire or installing a fire hood. When boxing in a luminaire, in the absence of any manufacturers’ guidance, a gap of about 100mm around the luminaire and 75mm above is recommended to allow for heat dissipation.
Downlighters in flats and maisonettes As mentioned earlier, in buildings containing flats or maisonettes, floors are constructed as fire compartment floors. However, suspended ceilings, comprising metal grids and plasterboard with voids of approximately three inches, are frequently installed for sound insulation and to hide services. Where suspended ceilings have been installed in flats and maisonettes, they can conveniently be utilised to install downlighters without fireproofing. In Scotland, the Building Regulations don’t allow downlighters to be installed in fire compartment ceilings if they are timber-based, unless a suspended ceiling has been provided. It is understood that this requirement is to reduce noise transmission between dwellings.
Installing downlighters in fire compartment ceilings For fire compartments to be effective, there must be continuity at the junctions of the fire-resisting elements that enclose them, and any openings from one compartment to another should not present a weakness. Section 9 of Approved Document B, ‘Fire Safety’ permits openings to be made in compartment walls and floors for certain purposes, including the passage of pipes, etc, that meet the provisions in Section 11. Clearly, the requirements of Approved Document B must be satisfied when installing downlighters in fire compartment ceilings. The advisability of keeping the number of downlighters in any one area to a minimum and to space them as far apart as possible was mentioned earlier but it is especially important when installing downlighters in fire compartment ceilings. As the period of fire resistance for fire compartment ceilings will be at least 60 minutes, it will be necessary to restore their fire resistance capability. The use of fire hoods or ‘boxing in’ of luminaries could be considered as a way of achieving this. Any openings remaining after the installation of downlighters must be sealed according to the degree of fire resistance required of the ceiling. The fire resistance of a fire compartment floor is typically 60 minutes but reference should be made Table A2 of the above document.
It should be pointed out that manufacturers’ instructions must be followed when installing downlighters. It is hoped that this article will prove helpful in the application of Regulation 527-02-01 to the installation of downlighters. For such installations, it is recommended that the local authority building control be consulted. Professional Engineering Technicians are involved in applying proven techniques and procedures to the solution of practical engineering problems. They carry supervisory or technical responsibility, and are competent to exercise creative aptitudes and skills within defined fields of Technology.
 

Reply to EICR & downlights in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
317
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
841
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
964

Similar threads

  • Question
I personally have two Integral Evofire Recessed (low-glare) on trial at home outside the UK; just realized they were, however, made of steel. The...
Replies
8
Views
658
I would C2 this, cable is not suitable for the environment its installed in, we would C2 a socket for equipment likely to be used outside , cable...
Replies
11
Views
954

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top