Mojo42

Still training so please be gentle!

During a practice of a EICR I found class 1 fittings on a lighting circuit. Cpc's present at light fitting, but cpc's not present on ALL of the switch drops. Some switches had metal back boxes others had none at all, just screwed into recess surrounded by wooden batton. Firstly can the switches be used without any back boxes, and providing only plastic switches are used can class 1 lights still be used?

Any advice much appreciated
 
The BS 7671-2008 in regulation 530.4.2 does not allow the use of plate switches etc to be fitted without a back box that complies to BS 4662 or BS 5733. This is not a new regulation and I would code the lack of back box as a 2.

Often in the past the use of a CPC was considered a "Luxury" when associated with a lighting circuit. I can still remember the older lads would cut the CPC out of a T+E on lights. I expect this is the case here. You most likely will find that the CPC as been snipped off at the light switch to stop it floating about.

You could see if there was slack and try and reconnect it, if you got enough slack you could crimp an extra piece on. If you do an R2 at the lights and confirm that the CPC is continuous from the light fitting back to the MET then you can leave them with no coding.

If you can't reconnect the CPC at the switch, and if all the switches are class II type then you could code it a 3.
 

Reply to EICR fault? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
332
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
859
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
983

Similar threads

It’s difficult to advise on an electrical issue when some isn’t very conversant with electrical terminology.
Replies
14
Views
1K
  • Question
There is no homework, and I'll never see these photo again.
Replies
3
Views
614

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top