Hi Guys,

need a a bit of advice. I was carrying out an EICR yesterday and when I came to test CU the fuse ways (12 of them) only had 5 of them labelled. The others were blank so I had no idea of what circuit the mcb's belong to. I tested IR on all circuits and all came back fine.

how do I record this on my EICR, do I leave the test sheet out and advise unable to carry out tests or is there another solution?

many thanks

dan
 
Hi Guys,

need a a bit of advice. I was carrying out an EICR yesterday and when I came to test CU the fuse ways (12 of them) only had 5 of them labelled. The others were blank so I had no idea of what circuit the mcb's belong to. I tested IR on all circuits and all came back fine.

how do I record this on my EICR, do I leave the test sheet out and advise unable to carry out tests or is there another solution?

many thanks

dan

It's quite common for CU's to be labeled incorrectly. I class working out what each is supplying as part of the EICR as you kind of need to know in order to test properly. You may come across 1 or 2 circuits which are sometimes impossible to identify and then I would just test IR and mark as unidentified, however I'm sure out of those 5 you could identify most of them with a little detective work :)
 
H guys

I would normally agree with you but it was ha early impossible. 12 mcbs 7x32a 2x20a 2x6a and 1x40a

i couldn't for the life of me find where the others were, I did as you said and tested ir and marked as u identified.

can I issue the cert with them marked like that?

thanks again
 
Hum.... I would say its YOUR responsibility, within the cost allowed for the job, to do it properly - and this includes identifying un labelled circuits.

How were you planning to proceed? What do you normally do?

AND more importantly, do you always "trust" what the labels say?
 
H guys

I would normally agree with you but it was ha early impossible. 12 mcbs 7x32a 2x20a 2x6a and 1x40a

i couldn't for the life of me find where the others were, I did as you said and tested ir and marked as u identified.

can I issue the cert with them marked like that?

thanks again

That's up to you and your agreement with the customer regards the scope of testing and limitations you previously agreed before starting the test.
I wouldn't issue it like that, just as I wouldn't IR test circuits that I had no idea where they went. How did you make the circuits suitable and safe for IR testing out of interest ?
 
I did advise te customer about them not being labelled and that I couldn't identify some of them. She was fine with it.

the house is empty and no LV lighting etc in there. What baffled me was there wasn't a great d Al of electrics in the place and one MCB I identified went to 1 socket in the hall (radial)

thats what hat I was up against
 
H guys

I would normally agree with you but it was ha early impossible. 12 mcbs 7x32a 2x20a 2x6a and 1x40a

i couldn't for the life of me find where the others were, I did as you said and tested ir and marked as u identified.

can I issue the cert with them marked like that?

thanks again

Hum... so back to basics - 12 circuits - how long did you allow for the EICR? and how long were you onsite?
 
for commercial premises, I get the customer to send a photo of the c/u before I start, this way problems like this are identified at the beginning.
I would discuss with customer and see what they want to do, you might be able to list them as operational limitations.
 
Should an experienced and qualified professional tester be persuading the customer to agree to half a job when it turns out he can't perform the testing to an adequate standard ? Or should he be calling on his knowledge and experience along with the site pre-assessment to allow enough time to complete the job in accordance with BS7671 and it's associated guidance ?
 
Last edited:
How can you not identify them?
The size of the MCB gives you a good rough starting point as to where you might find the circuits they're supplying.
32a - ring, cooker, outbuilding, shower
20a - more than likely going to be radial sockets
6a - more than likely going to be lights
40a - cooker, shower, outbuilding

whats the point in having an EICR done if you can't check it all properly.
I wouldn't personally be happy doing IR tests on anything if I didn't know where I was sticking my 500v.

I wouldn't care if the customer was happy with it being left like that or not - I wouldn't be. After all they're paying you because they don't know how to conduct the tests themselves. So if you tell her it's fine she will believe you but I don't think it is fine to leave it like that.

I aso aso wouldn't be happy if I was following you - doing work later or fault finding, coming across a nice shiney new date sticker on the CU only to open it up to find a load of unidentified circuits.
 

Reply to EICR help!! in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
296
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
804
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
840

Similar threads

  • Question
It sounds like they're buying a kellogs special K signature.
Replies
7
Views
820
Here the BPG#4 is useful, it is not a statutory document at all, but it provides good guidance as to what can reasonably considered as C1/C2/C3...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top