I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise.
I've just done an EICR on a flat and a few things that I didn't know how to code/address came up:
1) How do you code (and look for) inter-connected circuits? I found 2 socket ring-finals had only 21ohms between them (L-L, despite each testing fine individually (both ring-continuity and IR). Finding it was pure chance; the sockets were almost randomly on one circuit or another, so I plugged into the wrong one and was a bit concerned - how do you normally spot issues like this? From a safe isolation perspective, does this warrant a C2?
2) How can you do live tests on an economy-7 CU? I can't think of a way to sensibly get a Ipf/Ze for it, let alone RCD
3) Can meter tails be composite? 100A DNO fuse, fused down to 80A after the meter, then up to each flat. Am I right in thinking that once it's been fused to 80A, it's no longer a meter tail, just a regular circuit - and so can be reduced to a 16mm cable with 10mm earth?
And, they'd used 16mm T&E with a 10mm bonding taped on the side which seems cheap, but should be ok thermally as it's fused down, right?
4) The 2nd CU (for Economy7), was also fed in the same way (80A fused switch, 16mm T&E), but it had no 10mm earthing strapped on the side - just the internal 6mm CPC.
However, it did have a 10mm link from the MET in the previous CU over to this one, so indirectly it had 16mm. Is that a compliant way of supplying adequate earth, via multiple conductors with different paths? All plastic so no eddy current issues.
I've just done an EICR on a flat and a few things that I didn't know how to code/address came up:
1) How do you code (and look for) inter-connected circuits? I found 2 socket ring-finals had only 21ohms between them (L-L, despite each testing fine individually (both ring-continuity and IR). Finding it was pure chance; the sockets were almost randomly on one circuit or another, so I plugged into the wrong one and was a bit concerned - how do you normally spot issues like this? From a safe isolation perspective, does this warrant a C2?
2) How can you do live tests on an economy-7 CU? I can't think of a way to sensibly get a Ipf/Ze for it, let alone RCD
3) Can meter tails be composite? 100A DNO fuse, fused down to 80A after the meter, then up to each flat. Am I right in thinking that once it's been fused to 80A, it's no longer a meter tail, just a regular circuit - and so can be reduced to a 16mm cable with 10mm earth?
And, they'd used 16mm T&E with a 10mm bonding taped on the side which seems cheap, but should be ok thermally as it's fused down, right?
4) The 2nd CU (for Economy7), was also fed in the same way (80A fused switch, 16mm T&E), but it had no 10mm earthing strapped on the side - just the internal 6mm CPC.
However, it did have a 10mm link from the MET in the previous CU over to this one, so indirectly it had 16mm. Is that a compliant way of supplying adequate earth, via multiple conductors with different paths? All plastic so no eddy current issues.