Hi all.
I'm a little confused with what's correct here. I was told from a tradesman that any circuits in bath/shower area and circuits supplying mobile equipment that can be used outdoors that were not on an RCD were to be a code C2 when carrying out a EICR. Can someone with more knowledge on this please help me out here.
Thanks in advance
Hi all.
Thanks in advance
Have a read of this: http://www.esc.org.uk/fileadmin/use...y/best_practice/BestPracticeGuide4-Locked.pdf
Specifically page 15
Hi IQ Electrical.
It says in code C2 that
Absence of RCD protection for portable or mobile equipment that may reasonably be expected to be used outdoors
Would this stand for socket outlets on ground floor domestic EICR as they could potentially use the socket to supply mobile equipment outdoors?
Hi IQ Electrical.
Personally I wouldn't just apply that per se to every ground floor socket outlet but you could argue the case for RCD protection to be provided for a socket outlet near the back/front door or in a garage, all of which would be favourite for a lawnmower etc.
I was told from a tradesman that any circuits in bath/shower that were not on an RCD were to be a code C2 when carrying out a EICR.
Depends what circuit but say shower circuit C3
Edit : as tele says with bonding C3 without C2
C2 for outlet socket used for portable outdoor equipment without RCD
and a C2 for bathroom circuits without RCD and no supplementary bonding.
Hi all.
Thanks in advance
C3
Who is this "a tradesman" and what are you? Sparky or homeowner?
Reply to EICR info in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
This fella puts his face to it about halfway through, he has an opinion on the very subject.