I'm carrying out an EICR on a ex-council property. It's a low rise block with metal cabinets and an old 70's wylex CU.
few issues:
Single core cabling throughout.
There is no cpc on the lighting circuit. No cpc's on the metal backboxes on the plastic switches. All the pendants are plastic (classII). I can see a green cable behind one of the pendants but I'm not allowed to remove the pendants (decorations).
I understand that a cpc wasnt a regs requirement when installed.
How do I code it?
Is it ok if I just label it on the CU (black on yellow no metal fittings notice)
I can't ascertain what earth system is used. There's an earth terminal set into the back of the cupboard with a 10mm cpc to the CU. Can't remember what the Ze was but it was good, well within tolerance whatever the earth system is but I cant ascertain what type the earth system is. Can I omit the earth system info from the cert with an explanation?
Wish I hadnt touched it! nightmare client looking to rent to council, just wants a cert. Any advice gratefully rcd.
Cheers
s
few issues:
Single core cabling throughout.
There is no cpc on the lighting circuit. No cpc's on the metal backboxes on the plastic switches. All the pendants are plastic (classII). I can see a green cable behind one of the pendants but I'm not allowed to remove the pendants (decorations).
I understand that a cpc wasnt a regs requirement when installed.
How do I code it?
Is it ok if I just label it on the CU (black on yellow no metal fittings notice)
I can't ascertain what earth system is used. There's an earth terminal set into the back of the cupboard with a 10mm cpc to the CU. Can't remember what the Ze was but it was good, well within tolerance whatever the earth system is but I cant ascertain what type the earth system is. Can I omit the earth system info from the cert with an explanation?
Wish I hadnt touched it! nightmare client looking to rent to council, just wants a cert. Any advice gratefully rcd.
Cheers
s