OP. Recent EICR carried out at a Church & Hall. Would you code no SPD present at Supply origin & should the Lightning Protection System be connected to the Main Earthing Terminal via another SPD.
New Post. I see a Type 1 SPD was suggested at the origin of the supply.
As I understand Spd protection a Type 1 SPD is to prevent Flashover from a direct strike, causing break down of the insulation. Then a Type 2 is to prevent transient voltages to the rest of the installations sensitive equipment. The installation origin at the Church Hall is quite a distance from the LPS conductor & is not directly connected to the MET at present. I am limited for space for a standalone Type 1, I don't think the DNO would appreciate it on their External meter Box Board. As there is hardly any sensitive equipment other than a CD player for the Church service & an Office PC, I am inclined to install just a Type 2 in the main Consumer Unit. Do I need the Type 1 at the origin plus a Type 2 in the Consumer unit & what about the other 2 sub mains C/units? Obviously, there is a substantial price difference between the 2 devices. not much on the collection plate these days. Thanks guys for your input!