Good Morning All,
I will start by stating that the property concerned is a restaurant where I have now isolated the original electrical systems because of water ingress.
Being from Yorkshire we have been hit by flooding yet again recently and I have been asked to perform an EICR on a flooded property, to which I have answered "after some testing" that it will have to be a visual inspection for now as the building is still saturated and IR readings are in the main dead shorts because of the water ingress still present. Insurers being insurers want a concise report and are wanting to penny pinch and pass some of the cost of the peril onto the policy holder for non related items (fair enough I suppose for non related items) but they are directly effected by the water.
There are a couple of issues that I would appreciate a 2nd.....3rd or 4th opinion on from my fellow pros with regard as to how it can be worded to the insurers about the issues with no accurate test results and they are as follows.
1. Main area lighting is controled/switched by the 6a mcb's in the consumer unit, I don't like this but I suppose it is single pole switching in essence but I would prefer to rectify the issue.
2. The lighting circuit listed above also has some EM fittings which is obviously wrong and very poor installation as they will not be charging whilst the 6a mcb is isolated overnight, so to recify his I will be performing a modification to the circuit (does this have an impact on item 1 above?).
3. Lack of RCD protection on this installation that was installed to the 16th edition of BS7671, my concern here is that I will be isolating and improving some cabling but the insurer does nor want to foot a CU upgrade, but yet again this is required because of the water ingress that some remedial work is required.
4. Not 100% sure on this one but the lighting itself is 12v spots that are not fire rated, now I know that if there is a bedroom above they should "now" be fire rated so is this the case if there is an office unit above the lighting? The lighting requires changing because of water pitting but the insurer wants to replace with non fire rated fittings and I am not happy to do so.
5. Non accessible JB's on a 16th edition installation "why on earth does anyone ever do this?"
Your input on how I can word this to the insurer would be greatly appreciated guys.
Regards SYKRAPS.
PS I will not be able to answer any questions that you may have until later in the day as I have to go to now worst luck.
I will start by stating that the property concerned is a restaurant where I have now isolated the original electrical systems because of water ingress.
Being from Yorkshire we have been hit by flooding yet again recently and I have been asked to perform an EICR on a flooded property, to which I have answered "after some testing" that it will have to be a visual inspection for now as the building is still saturated and IR readings are in the main dead shorts because of the water ingress still present. Insurers being insurers want a concise report and are wanting to penny pinch and pass some of the cost of the peril onto the policy holder for non related items (fair enough I suppose for non related items) but they are directly effected by the water.
There are a couple of issues that I would appreciate a 2nd.....3rd or 4th opinion on from my fellow pros with regard as to how it can be worded to the insurers about the issues with no accurate test results and they are as follows.
1. Main area lighting is controled/switched by the 6a mcb's in the consumer unit, I don't like this but I suppose it is single pole switching in essence but I would prefer to rectify the issue.
2. The lighting circuit listed above also has some EM fittings which is obviously wrong and very poor installation as they will not be charging whilst the 6a mcb is isolated overnight, so to recify his I will be performing a modification to the circuit (does this have an impact on item 1 above?).
3. Lack of RCD protection on this installation that was installed to the 16th edition of BS7671, my concern here is that I will be isolating and improving some cabling but the insurer does nor want to foot a CU upgrade, but yet again this is required because of the water ingress that some remedial work is required.
4. Not 100% sure on this one but the lighting itself is 12v spots that are not fire rated, now I know that if there is a bedroom above they should "now" be fire rated so is this the case if there is an office unit above the lighting? The lighting requires changing because of water pitting but the insurer wants to replace with non fire rated fittings and I am not happy to do so.
5. Non accessible JB's on a 16th edition installation "why on earth does anyone ever do this?"
Your input on how I can word this to the insurer would be greatly appreciated guys.
Regards SYKRAPS.