M

mpatto

hello all, help needed please.
no paper work at all with this install, 7 years old.
will i need to do full tests on every circuit then for EICR?
will ph+n linked - cpc insulation (500v) test be sufficient? will that blow 12v transformers and dimmers?

thanks
 
For any EICR you should do 100% testing, whenever possible.
Inspections can be reduced from 100% if the installation is in good condition (minimum 10%).

An IR test with L+N to E is OK for an EICR and should not affect dimmers and transformers but may affect some other electronics, test at 250V first to see if the reading is low and this may indicate a problem that you should resolve before testing at 500V.
 
As Richard says, every circuit should be TESTED during an EICR. Then, depending on the results, it is up to you to decide how far to go with the inspection side of things. For example, if you get a bad result on one particular circuit, then you will really need to drill down and thoroughly inspect that circuit...
 
All equipment vulnerable to testing should be removed from the circuits, and a temporary link put in, in its place to keep the circuit continuous.

I dont want to pee on your bonfire mate, nor do i want to put you off doing the work, we all had to learn at sometime, and that usually meant doing it with someone more experienced. If you dont know what damage you could do to certain accessories, and are not too sure of the testing procedures, then to save yourself getting a red face and/or a big bill, i would be asking for someone to show me the ropes.

Cheers...........Howard
 
Im with the above two. The insulation resistance alone can give a very good indication on the condition of the installation. However if you are asking if you have to remove runnable / Sensitive equipment i think you could be learning that it can also be an expensive testing procedure im affraid.
 

Reply to EICR on existing install in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
330
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
855
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
975

Similar threads

In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K
Interesting question & always gonna get different views on this. EICR testing seems to have changed over the years & not by us the Electricians...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top