DB has redundant cables connected to protective devices!
Any reg in the 18th??? Memory recalls (badly) something in GN4
DB has redundant cables connected to protective devices!
Any reg in the 18th??? Memory recalls (badly) something in GN4
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss EICR Redundant cables in DB, MCB taped over! in the UK Electrical Forum area at ElectriciansForums.net
Yes they were connected, was looking for a reg.Lol, so not an issue anymore ? I'm confused, you previously said they were connected.
Yes they were connected, was looking for a reg.
And not relying on something from GN4
[automerge]1594403835[/automerge]
is everybody here just trying to beat me up? And not actually give any help?
Jeesus
And earth them, was your reply, which is correct.I said in post 6 about disconnecting them. You never said you had done this.
It's hard work this.
And earth them, was your reply, which is correct.
This moment in time, they are just disconnected.
Yeah really hard work, aint it.
Redundant cables; connect them to earth or pull em out.
This would ‘prevent danger so far as is reasonable practicable’ in the spirit of Regulation 130-02-01.
Regulation 130-02-01
'Persons and livestock shall be protected so far as is reasonably practicable against dangers that may arise from contact with live parts of the installation'
That aside I don't believe there is an explicit reg about terminating unused cables to earth.
You could use the above for them no? If they're live and just dangling like a duck then you are not meeting the requirements of 130-02-01I think he was wanting a reg regarding live bare cables.
Immediate action was to disconnect, as per code 1.Redundant cables; connect them to earth or pull em out.
This would ‘prevent danger so far as is reasonable practicable’ in the spirit of Regulation 130-02-01.
Regulation 130-02-01
'Persons and livestock shall be protected so far as is reasonably practicable against dangers that may arise from contact with live parts of the installation'
That aside I don't believe there is an explicit reg about terminating unused cables to earth.
Immediate action was to disconnect, as per code 1.
Thank you for providing a reg, that is all I wanted.
Remedial works would be to totally the remove the cabling including neutrals which would have to be properly identified. Failing that, an enclosed box would need to fitted, with fixed based connectors clearly identified, and put to earth.
All I want is a reg number cupcake, as per the OPBut hasn't that last option not already been done?
You can't assume it has - so can't ignore it.
You can't assume it hasn't so can't code C1, C2, or C3.
Without knowing what the actual issue is, it becomes FI.
If you do know the wires are unterminated, and left hanging potentially live, then it would be C1 if exposed to the touch, C2 if in something, but not in a good way, perhaps C3.
The actual regulation would depend upon the actual issue.
All I want is a reg number cupcake, as per the OP
Read the thread in its entirety. Thank you