EICR

DB has redundant cables connected to protective devices!
Any reg in the 18th??? Memory recalls (badly) something in GN4
 
Why would it be a C1 even if it was connected?

I have the wiring for a future shower connected in the cu, at the other end local to the future shower placement the wiring is terminated in a mf box ready to use.

The only thing that could ever warrant would be a FI should the person doing the periodic not be bothered to look for the other end.

And yes, on occasion I put a bit of tape across all the off rcbos as if something trips, it's then easy to see which one is in the "wrong" position - more for the convenience of others than mine.

The tape over the mcb doesn't automatically mean it's an attempt at isolation.
 
Yes they were connected, was looking for a reg.
And not relying on something from GN4
[automerge]1594403835[/automerge]
is everybody here just trying to beat me up? And not actually give any help?
Jeesus

Chill man, I was just trying to establish what the actual issue is. If you've disconnected it there is no issue as you will have left it safely connected to the earth bar.
If it's still connected then you can't possibly code it first without establishing if it is contravening a regulation that impacts on the safety of the installation. If you've not done this then it's FI required.
 
Redundant cables; connect them to earth or pull em out.

This would ‘prevent danger so far as is reasonable practicable’ in the spirit of Regulation 130-02-01.

Regulation 130-02-01
'Persons and livestock shall be protected so far as is reasonably practicable against dangers that may arise from contact with live parts of the installation'

That aside I don't believe there is an explicit reg about terminating unused cables to earth.
 
Redundant cables; connect them to earth or pull em out.

This would ‘prevent danger so far as is reasonable practicable’ in the spirit of Regulation 130-02-01.

Regulation 130-02-01
'Persons and livestock shall be protected so far as is reasonably practicable against dangers that may arise from contact with live parts of the installation'

That aside I don't believe there is an explicit reg about terminating unused cables to earth.

I think he was wanting a reg regarding live bare cables.
 
I think he was wanting a reg regarding live bare cables.
You could use the above for them no? If they're live and just dangling like a duck then you are not meeting the requirements of 130-02-01

ETA; obviously if they're dead then at best I'd go a C3; they have the potential to become live but would require something else to happen first
 
Redundant cables; connect them to earth or pull em out.

This would ‘prevent danger so far as is reasonable practicable’ in the spirit of Regulation 130-02-01.

Regulation 130-02-01
'Persons and livestock shall be protected so far as is reasonably practicable against dangers that may arise from contact with live parts of the installation'

That aside I don't believe there is an explicit reg about terminating unused cables to earth.
Immediate action was to disconnect, as per code 1.
Thank you for providing a reg, that is all I wanted.
Remedial works would be to totally the remove the cabling including neutrals which would have to be properly identified. Failing that, an enclosed box would need to fitted, with fixed based connectors clearly identified, and put to earth.
 
Immediate action was to disconnect, as per code 1.
Thank you for providing a reg, that is all I wanted.
Remedial works would be to totally the remove the cabling including neutrals which would have to be properly identified. Failing that, an enclosed box would need to fitted, with fixed based connectors clearly identified, and put to earth.

But hasn't that last option not already been done?

You can't assume it has - so can't ignore it.
You can't assume it hasn't so can't code C1, C2, or C3.

Without knowing what the actual issue is, it becomes FI.

If you do know the wires are unterminated, and left hanging potentially live, then it would be C1 if exposed to the touch, C2 if in something, but not in a good way, perhaps C3.

The actual regulation would depend upon the actual issue.
 
But hasn't that last option not already been done?

You can't assume it has - so can't ignore it.
You can't assume it hasn't so can't code C1, C2, or C3.

Without knowing what the actual issue is, it becomes FI.

If you do know the wires are unterminated, and left hanging potentially live, then it would be C1 if exposed to the touch, C2 if in something, but not in a good way, perhaps C3.

The actual regulation would depend upon the actual issue.
All I want is a reg number cupcake, as per the OP
Read the thread in its entirety. Thank you
 

Reply to EICR Redundant cables in DB, MCB taped over! in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
953
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
782
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
957

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top