EICR report refused for C2 condition of earthing. How to rectify if i even ned to. | on ElectriciansForums

Discuss EICR report refused for C2 condition of earthing. How to rectify if i even ned to. in the UK Electrical Forum area at ElectriciansForums.net

P

paulwalldall

Hi. Niece had an inspection prior to letting out her house and recieved a number of C2 decisions on earthing. such as "earth cable to TN-S not large enough." Wants to change to 16mm. no bonding to inlet services at all. (fair enough on this one). Question is , Ive only qualified after 3yr course at college (i,m 45 yrs old) got 2394 , inspection testing, got multitester and tools. If i do the changes so it "complies with current regs" would i have to be registered with local authority or niceic or can the chap come back , re-test and tick the boxes. Quick answer appreciated as going out very soon.
 
Re: EICR report refused for C2 condition of earthing. How to rectify if i even ned to

nothing to stop you doing the remedials, then do her a EICR with no C2's, or complete a EIC for the remedials and reference to the existing EICR.
 
Re: EICR report refused for C2 condition of earthing. How to rectify if i even ned to

Why is the 16mm earthing conductor required?
Has the Inspector done an adiabatic to confirm that 16mm is required?
Have a read of 543.1.4, do a PFC and PEFC, then work it out, and I'd bet a 16mm earthing conductor will not be necessary.

You will need to put in some bonding for gas/water/other services.
 
Re: EICR report refused for C2 condition of earthing. How to rectify if i even ned to

don't be messing about with the clamp for the main earth, if it does turn out that it needs replacing then phone the dno and they'll upgrade it.
 
Re: EICR report refused for C2 condition of earthing. How to rectify if i even ned to

I can almost guarantee that the main earth doesn't need upgrading. The only way this would be so is if the OP had either an extremely high PFC or an extremely low PFC. Neither case is likely.
 
Re: EICR report refused for C2 condition of earthing. How to rectify if i even ned to

Any chance of a pic I bet its from the MET to the CU that he has given the code 2 and post 4 has answered that issue.

Out of interest did he refer to any regulation and on the Condition Report Inspection Schedule which item number did he highlight and put C2 against ?
 
Re: EICR report refused for C2 condition of earthing. How to rectify if i even ned to

he's only miffed because he wasn't included in HHD's hall of fame.
 
Re: EICR report refused for C2 condition of earthing. How to rectify if i even ned to

he's only miffed because he wasn't included in HHD's hall of fame.

He was!!
 
Re: EICR report refused for C2 condition of earthing. How to rectify if i even ned to

must have missed that, laffing so much, my bad.
 
Re: EICR report refused for C2 condition of earthing. How to rectify if i even ned to

Thanks for replies. having seen the house today as i live 60 miles away. i can confirm the earth requiring upgrading is indeed from the incoming supply to earth terminal in cu box. it looks only 6mm at the mo so will do sums to see if acceptable but not sure of breaker types or ze from here. as for bonding to gas/water, checked where supplies are and gas is out front of house and water in the back in kitchen cupboard, cu in dead center of house under stairs. just curious but can i bond to gas pipe as it enters rear of house near to water supply as its a lot easier.(sounds a bit lazy). its only feed is into kitchen then rear of house for boiler.
 

Reply to EICR report refused for C2 condition of earthing. How to rectify if i even ned to. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
349
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
896
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top