Did an EICR today as soon as I walked in lots of things failed.

However what got me thinking the most was the fact that every room was fed from its own circuit breaker 3 bed flat all on 15A mcb's each room contained 2 double sockets. But these sockets where fed from 1.5mm twin and earth. Are these really as much of a hazard as universally thought? Considering each room is protected by its own mcb?

Worst thing I did see though was unbelievably was a junction box of the kitchen ring in 2.5mm out if that came a 4mm twin an earth feeding the cooker switch
 
IMO the sockets are safe provided that disconnection times for the MCB is met, and there is no insulation. If I remember correctly, 1.5 is good for 16A, obviously this is without any derating, but if the cables are clipped direct under plaster, at less than 30 deg, no insulation, then it should be ok.
 
The Ring at the end of a 4mm cable is not a recognised standard install.

I think the OP means that there's a spur off the 2.5mm² ring feeding the cooker switch in 4mm².

Nothing really wrong with it if the cooker is plug and socket type. However it's recommended that anything over 2kW to be on it's own dedicated circuit
 
Did an EICR today as soon as I walked in lots of things failed.

However what got me thinking the most was the fact that every room was fed from its own circuit breaker 3 bed flat all on 15A mcb's each room contained 2 double sockets. But these sockets where fed from 1.5mm twin and earth. Are these really as much of a hazard as universally thought? ??? As already said 2x, nowt wrong with these. Considering each room is protected by its own mcb? The anti RFC brigade will like this.

Worst thing I did see though was unbelievably was a junction box of the kitchen ring in 2.5mm out if that came a 4mm twin an earth feeding the cooker switch Depending on the the Cooker load, maybe a C3...

??????????????????????????????????
 
Yes thats right cooker fed off kitchen ring. Looks to be over 2kw.

I though sockets would be ok.

However major issues elsewhere. Ip ratings on consumer units non existant. Finger and tool ingress on everyone of the seperate consumer units.

Socket outlet in bathroom feeding heater 1m away from bath. Bonding is literally 1mm earth.

All earths have been cut out of consumer units but at each socket outlet I get a Zs. Must be earthed elsewhere?

- - - Updated - - -

Yes thats right cooker fed off kitchen ring. Looks to be over 2kw.

I though sockets would be ok.

However major issues elsewhere. Ip ratings on consumer units non existant. Finger and tool ingress on everyone of the seperate consumer units.

Socket outlet in bathroom feeding heater 1m away from bath. Bonding is literally 1mm earth.

All earths have been cut out of consumer units but at each socket outlet I get a Zs. Must be earthed elsewhere?
 
I think the OP means that there's a spur off the 2.5mm² ring feeding the cooker switch in 4mm².

Nothing really wrong with it if the cooker is plug and socket type. However it's recommended that anything over 2kW to be on it's own dedicated circuit

If it is as you say then you are quite correct.

But if its going to the cooker switch and then to a cooker connection outlet,
then that's un-acceptable as some one could connect a load more than 2KW(hob/Oven) to it,
instead of just using it as an igniter socket.
 
Yes thats right cooker fed off kitchen ring. Looks to be over 2kw.

I though sockets would be ok.

However major issues elsewhere. Ip ratings on consumer units non existant. Finger and tool ingress on everyone of the seperate consumer units.

Socket outlet in bathroom feeding heater 1m away from bath. Bonding is literally 1mm earth.

All earths have been cut out of consumer units but at each socket outlet I get a Zs. Must be earthed elsewhere?

- - - Updated - - -

Yes thats right cooker fed off kitchen ring. Looks to be over 2kw.

I though sockets would be ok.

However major issues elsewhere. Ip ratings on consumer units non existant. Finger and tool ingress on everyone of the seperate consumer units.

Socket outlet in bathroom feeding heater 1m away from bath. Bonding is literally 1mm earth.

All earths have been cut out of consumer units but at each socket outlet I get a Zs. Must be earthed elsewhere?


Is the Kitchen on a Ring?(r1,r2 & rn?)

4mm spur to Cooker switch must be a C2

No sockets allowed in the bathroom,C3M

Check the bonding and earthing,
 

Reply to EICR sockets in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
275
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
773
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
779

Similar threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
769
Hello Ric2013, MJPD29 and westward 10. I have a multimeter that I tested the voltage with and before I open the socket up I use a plug in tester...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top