Doing inspections today and found a couple of properties with under sized earthing and bonding conductors. Earthing system is TNC-S and features 6mm earthing conductor and 6mm bonding conductors.
I normally code 6mm bonding conductors as C3 and am happy to do so here too, but should I be coding the small earthing conductor more harshly ?
It will not conform with 542.3.1 as the earthing conductor will not be at least the size of the required size for the bonding conductor, but the bonding conductors are not of the required size anyway. The size does conform with the adiabatic equation for thermal constraints.
Could do with some helpful thoughts as I have a couple dozen of these to do and they look like they might all be of similar construction.
They are all looking at board upgrades anyway so this may be academic, but would like to be coding correctly.
I normally code 6mm bonding conductors as C3 and am happy to do so here too, but should I be coding the small earthing conductor more harshly ?
It will not conform with 542.3.1 as the earthing conductor will not be at least the size of the required size for the bonding conductor, but the bonding conductors are not of the required size anyway. The size does conform with the adiabatic equation for thermal constraints.
Could do with some helpful thoughts as I have a couple dozen of these to do and they look like they might all be of similar construction.
They are all looking at board upgrades anyway so this may be academic, but would like to be coding correctly.