I would be more concerned about the three electric showers.

I can't make out all the MCB markings for sure, but it looks like on this 80A-rated RCD, there are 4x32A socket ring final circuits, and 3x40A shower circuits. Despite applying diversity, might there not be the risk of this RCD getting a little overloaded, if more than one person is taking a shower at once?
 
I would class the wrong MCBS as a code 2 - they not designed for the DB
could someone enlighten me as to why a mixture of different MCB's should be coded at all? If they are marked as conforming to BS60898 and physically fit properly what difference does it make? It can't possibly be a code 2
 
could someone enlighten me as to why a mixture of different MCB's should be coded at all? If they are marked as conforming to BS60898 and physically fit properly what difference does it make? It can't possibly be a code 2
it states in manufacturer's instructions to only use there breakers, bs7671 says you need to take manufacturer's instructions into account
 

Reply to EICR What would you do? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
852

Similar threads

I usually put something like this To assess compliance with BS7671 for continued safe operation (5 year periodical inspection)
Replies
8
Views
441
Thanks for the reply littlespark. Yes the works have been carried out. Surely it is fraudulent because basically the document is Not...
Replies
2
Views
710

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top