Really well there you go, would never have thought it.

Where I can guarantee that the cable is fine for 32A, which is quite often in domestic rewires/refurbs, it's a no brainer really.
The situation the OP has where there is a separate oven and hob supply is also more common due to people wanting them in different locations on a kitchen fit. A 6mm to each is not really warranted in that case.

In the OP's situation I have to say that I would be tempted to drop the MCBs down to 20A or 25A though, dependant on measured current draw of the installed appliances and manufacturer's guidance.
No-one can rightly say that the 4mm installed is or isn't suitable for a 32A OCPD, although a reduction in MCB size could help with safety concerns. Certainly a lot easier than pulling in new 6mm cables for an uncertain safety issue.
 
Call me an old traditionalist, but in general terms I would install a 6mm for a cooker circuit (i.e. 32a supply) & 10mm for a shower circuit (40a supply) in the absence of any known appliance. Otherwise, the home owner may have to rewire that circuit ever time they get a new cooker or shower, or when there's a change of ownership.

That said, my really expensive Hotpoint Range cooker :rolleyes:, has 1.00mm flex (manufactures). So I could probably run that off the lighting circuit. I'd better go turn it on now, to warm it up for the roast dinner!
Good shout,but in the old days,this was fine,& I certainly wouldn't want to rewire it in 6.0 mm for the sake of it.
 
Where I can guarantee that the cable is fine for 32A, which is quite often in domestic rewires/refurbs, it's a no brainer really.
The situation the OP has where there is a separate oven and hob supply is also more common due to people wanting them in different locations on a kitchen fit. A 6mm to each is not really warranted in that case.

In the OP's situation I have to say that I would be tempted to drop the MCBs down to 20A or 25A though, dependant on measured current draw of the installed appliances and manufacturer's guidance.
No-one can rightly say that the 4mm installed is or isn't suitable for a 32A OCPD, although a reduction in MCB size could help with safety concerns. Certainly a lot easier than pulling in new 6mm cables for an uncertain safety issue.
Cheers for your remarks,all taken on board.
 

Reply to Eicr in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
563
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
998
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
937

Similar threads

The challenge that you have with this is that you've no confirmed start point. Because you have a lack of an EICR you don't actually know what...
Replies
7
Views
741

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top