Really well there you go, would never have thought it.I have, plenty of times. Obv
iously it's reference method dependant though.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Eicr in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Really well there you go, would never have thought it.I have, plenty of times. Obv
iously it's reference method dependant though.
CheapskateI have, plenty of times. Obviously it's reference method dependant though.
Really well there you go, would never have thought it.
Ha, it's more to do with ease of installation and connection.Cheapskate
Good shout,but in the old days,this was fine,& I certainly wouldn't want to rewire it in 6.0 mm for the sake of it.Call me an old traditionalist, but in general terms I would install a 6mm for a cooker circuit (i.e. 32a supply) & 10mm for a shower circuit (40a supply) in the absence of any known appliance. Otherwise, the home owner may have to rewire that circuit ever time they get a new cooker or shower, or when there's a change of ownership.
That said, my really expensive Hotpoint Range cooker , has 1.00mm flex (manufactures). So I could probably run that off the lighting circuit. I'd better go turn it on now, to warm it up for the roast dinner!
Cheers for your remarks,all taken on board.Where I can guarantee that the cable is fine for 32A, which is quite often in domestic rewires/refurbs, it's a no brainer really.
The situation the OP has where there is a separate oven and hob supply is also more common due to people wanting them in different locations on a kitchen fit. A 6mm to each is not really warranted in that case.
In the OP's situation I have to say that I would be tempted to drop the MCBs down to 20A or 25A though, dependant on measured current draw of the installed appliances and manufacturer's guidance.
No-one can rightly say that the 4mm installed is or isn't suitable for a 32A OCPD, although a reduction in MCB size could help with safety concerns. Certainly a lot easier than pulling in new 6mm cables for an uncertain safety issue.
Why its only a couple of quid.Good shout,but in the old days,this was fine,& I certainly wouldn't want to rewire it in 6.0 mm for the sake of it.
What do you deem as the "old days"Good shout,but in the old days,this was fine,& I certainly wouldn't want to rewire it in 6.0 mm for the sake of it.
1970's the good old days then,only cos we were younger I guess.What do you deem as the "old days"
Why its only a couple of quid.
But would it be only a couple of quid.Why its only a couple of quid.
Reply to Eicr in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net