We have installed several electric boilers of this size and have always had to have fuses/ supply upgraded to 100amp at customers expense. When we first fitted one it was fired up and hob and oven were put on at same time and it was drawing 82amps so upgrade is a must. 12kw is usually ok for three bedroom semi and hot water but anymore than that and it will struggle. If you use an Amptec boiler you can purchase a relay that cuts power to the boiler if an electric shower is turned on which can be useful. You also need to bear in mind that any isolators need to be able to cope with the 52 amps the boiler will draw as well. Hopefully you will be as amused as we were to see the speed the meter wheel spins at when the boiler is in use. If it is a combined boiler and hot water system, eg Heatrae Sadia Electromax, the hot water is provided via two immersion which heaters and an unvented cylinder which will add more demand supply.