Hello,

I have just moved into a new house, which will require a full rewire.

I am looking at relocating the main electrical consumer unit into the boiler room which houses the gas combi boiler.

Can anyone advise any regulations that would resrict this?


Thanks,

Callum
 
It's fine to be in the same room. Try to keep consumer unit a minimum of 300mm from boiler not a requirement just good practice but other than that its fine

I would say it could well be a requirement, reg 528.3.4 refers to the gas regs BS 6891. Minimum separation is also mentioned in the OSG. 150mm from the consumer unit or the use of suitable barrier if I'm not mistaken.
 
Suitable barrier from a boiler? Are you sure your not referring to to the incoming gas supply. I take 300mm as good practice

I certainly wouldn't disagree that 300mm is good practice I'm just pointing out that there are regs stating 150mm (6 inches) separation of the consumer unit from gas installations as a minimum.

from 8.16.2 of BS 6891
where installation pipes are not separated by electrical insulating material they shall be spaced as follows
a) at least 150mm from electricity meters and associated excess current controls ,electrical switches or sockets, distribution boards or consumer units.
 
I certainly wouldn't disagree that 300mm is good practice I'm just pointing out that there are regs stating 150mm (6 inches) separation of the consumer unit from gas installations as a minimum.

from 8.16.2 of BS 6891
where installation pipes are not separated by electrical insulating material they shall be spaced as follows
a) at least 150mm from electricity meters and associated excess current controls ,electrical switches or sockets, distribution boards or consumer units.

Thanks guys - so if I keep the CU atleast 150mm from both pipework & boiler then I should be ok.

Do I need to have an electrical insulating material mounted on the wall ready for the electrician to mount the CU onto? Or is this not a requirement?
 

Reply to Electric Consumer Unit allowed in Boiler cupboard? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
766
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
771

Similar threads

  • Question
IMO Better to do something about those ignoring regulations first! Current system is like having a speed limit but not enforcing anyone without a...
2
Replies
20
Views
2K
  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
769

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top