Had a really odd problem out on a job the other day and wondered if others have encountered the same and what they did!
Large rural plot with house, outbuildings and lots of land. TT, but on a dedicated pole which is PME so not sure what happened there!
When doing some ground works and digging up some old oil pipes (I was there to wire in a sewage system...nice.....) we noticed that the underground copper was all 'live', ie if you touched it you got a shock. Got my meter on it and couldn't find anything, though, very odd. Defo a 'throb tingle' there when you put your hand to it but not strong enough to be a danger and definitely not mains voltage or frequency. This continued INSIDE the house and you could feel it through the stainless kitchen sink. I checked all the bonding, metered the place right through and couldn't find an installation fault anywhere.
Eventually, after 2 hours......
They have an enormous big duck pond, various animal pens etc all protected by one very long electric fence. And it turned out it was feeding back via the actual ground itself where it was touching (as it's meant to...) and therefore creating a loop via the TT earthstakes back into the main installation. So.... in a reverse of the normal situation the more rods you bang into the ground, the worse it gets!! The fence controller itself was fine (double insulated) and everything was working 'as designed and intended'. I think it's just the extremely conductive soil we get around here in Somerset (very wet and peaty). I eventually made the problem go away by banging a whole load of earth rods in all around the perimeter of the fence and then installing a great long return loop back to the fence controller, but that's not really how they're meant to work!!
Thoughts, anyone?
Large rural plot with house, outbuildings and lots of land. TT, but on a dedicated pole which is PME so not sure what happened there!
When doing some ground works and digging up some old oil pipes (I was there to wire in a sewage system...nice.....) we noticed that the underground copper was all 'live', ie if you touched it you got a shock. Got my meter on it and couldn't find anything, though, very odd. Defo a 'throb tingle' there when you put your hand to it but not strong enough to be a danger and definitely not mains voltage or frequency. This continued INSIDE the house and you could feel it through the stainless kitchen sink. I checked all the bonding, metered the place right through and couldn't find an installation fault anywhere.
Eventually, after 2 hours......
They have an enormous big duck pond, various animal pens etc all protected by one very long electric fence. And it turned out it was feeding back via the actual ground itself where it was touching (as it's meant to...) and therefore creating a loop via the TT earthstakes back into the main installation. So.... in a reverse of the normal situation the more rods you bang into the ground, the worse it gets!! The fence controller itself was fine (double insulated) and everything was working 'as designed and intended'. I think it's just the extremely conductive soil we get around here in Somerset (very wet and peaty). I eventually made the problem go away by banging a whole load of earth rods in all around the perimeter of the fence and then installing a great long return loop back to the fence controller, but that's not really how they're meant to work!!
Thoughts, anyone?