Hi good evening I was asked to preform a EICR on a reasonably new flat built in 1990. The testing and inspection went as planned apart from one glaring anomaly. The bathroom has a electric fan heater operated by a switch on the side. It is positioned above the rear of the bath with no shower. The owner mentioned this has been there since the flat was built.
[ElectriciansForums.net] Electric  heater  Zone 1 Bathroom
The question is when this was installed would this have complied with previous incarnations of the 17th?
Regards

RichardG
 
I would also say C2. However without a shower the risk is fairly low, but a definite contravention of the current regulations.
23 years old is not too new and would have been installed to 15th Edition.
I believe that the regulations have become easier in some ways for bathrooms and I am fairly sure standard switches were not permitted in zone 1.
 
The question is when this was installed would this have complied with previous incarnations of the 17th?

It didn't comply with any incarnation of the 17th - I presume you mean earlier Editions?

Either way, I don't see the relevance. You are assessing the safety and suitability for continued service. Does it make it any more or less unsafe if it was permitted before? You are inspecting to the current edition of the Regulations, i.e. BS 7671:2008 incorporating Amendment No. 2 (2013) (and not forgetting the recent Corrigendum!)
 
I agree code C2, however I would describe that as zone 2 see Fig 701.1 a in BGB. Zone 1 ends at the end of the bathtub. Either way fused outlet is not suitable for the zone and I suspect heater is not IPX4 rated.
 

Reply to Electric heater Zone 1 Bathroom in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
478
  • Question
Thanks Brian, That makes sense, just in case someone bangs a nail in ⚡️
2
Replies
39
Views
5K
It's going to be a right pain switching the towel radiator on and off every single time you want to use it. I always fit a timer (standard analog...
Replies
2
Views
4K
  • Question
Nice one, thanks for letting us know.
2
Replies
34
Views
8K
I find with these so called 'class 2' metal light fittings which are basically class 1 fittings with a crappy supposedly double insulated joint...
    • Funny
    • Like
Replies
20
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks