Here's one for a Sunday. I need some advice please.
I went to quote for a job yesterday, where my client is replacing the aged electric convector panel heaters in her flat with some new electric radiators.
I was asked to remove one of the old ones. All the existing heaters are connected to FCU's. Having done a visual inspection of the supply circuit, I noted it was in fact a dedicated 32A RFC (i.e. only used for the heaters), wired in 2.5mm tw&e, as opposed a 32A radial.
The current load is 3750w, made up of 3 x 1000w & 1 x 750w (16.3A @ 230v). The new load would be 4750w, made up of 1 x 2000w, 2 x 1000w & 1 x 750w (20.6A @ 230v). These new heaters have been chosen by the manufacturers, by the dimensions of each room etc.
I understand appendix 15 gives guidance on not supplying electric space heating on RFC's, and reg 433.1.204 (on RFC's) 'if the current carrying capacity of the cable is not less than 20A... etc'.
The reference method would I guess be A, giving a ccc of 20A for 2.5mm.
Your thoughts?
I went to quote for a job yesterday, where my client is replacing the aged electric convector panel heaters in her flat with some new electric radiators.
I was asked to remove one of the old ones. All the existing heaters are connected to FCU's. Having done a visual inspection of the supply circuit, I noted it was in fact a dedicated 32A RFC (i.e. only used for the heaters), wired in 2.5mm tw&e, as opposed a 32A radial.
The current load is 3750w, made up of 3 x 1000w & 1 x 750w (16.3A @ 230v). The new load would be 4750w, made up of 1 x 2000w, 2 x 1000w & 1 x 750w (20.6A @ 230v). These new heaters have been chosen by the manufacturers, by the dimensions of each room etc.
I understand appendix 15 gives guidance on not supplying electric space heating on RFC's, and reg 433.1.204 (on RFC's) 'if the current carrying capacity of the cable is not less than 20A... etc'.
The reference method would I guess be A, giving a ccc of 20A for 2.5mm.
Your thoughts?