K

kadelec

Hi. Just a quick question. Got a job coming up which is just swapping a shower over. Old rewireable CU. Anyway the gas and water is earthed in 6mm earth. I'm upgrading main earth to 16mn . Do I need to upgrade these to 10mm? And obviously put the current circuit on an rcd. Thanks in advance.
 
hi. Just a quick question. Got a job coming up which is just swapping a shower over. Old rewireable cu. Anyway the gas and water is earthed in 6mm earth. I'm upgrading main earth to 16mn . Do i need to upgrade these to 10mm? not if they show no signs of thermal damage and are intact.

and obviously put the current circuit on an rcd. yes


what's the earthing system?
 
What's wrong with the existing earthing conductor?
What size bonding does the installation require
Is the existing bonding in good condition?
 
Manufacturers recommendation. Mira have it down as not recommended because of inadequate short circuit capacity (see reg 433.1.3) and Triton have it down as DO NOT use a rewireable fuse.
 
Manufacturers recommendation. Mira have it down as not recommended because of inadequate short circuit capacity (see reg 433.1.3) and Triton have it down as DO NOT use a rewireable fuse.

Fine, but why do you believe it shouldn't be used?

It is perfectly possible to install a fully compliant installation which uses 3036 fuses for its ocpds
 
the regs now say to take manufacturer's instructions under advisement not to blindly follow them.

i would offer the option of the rcd by saying it would make it safer or to use the existing supply
 
Fine, but why do you believe it shouldn't be used?

It is perfectly possible to install a fully compliant installation which uses 3036 fuses for its ocpds

Come on Dave, you're hot on current electrical terminology so why use a method of protection that belongs in the past ? Would you really use a rewireable fuse to provide over current and short circuit protection on a shower circuit ?
 
Come on Dave, you're hot on current electrical terminology so why use a method of protection that belongs in the past ? Would you really use a rewireable fuse to provide over current and short circuit protection on a shower circuit ?

On a new circuit no, but I see no reason to comment if an existing shower circuit uses a 3036 fuse for protection
 
If it was me I'd say no unless it was going on an RCD, I accept what you all have to say but I would just sleep a bit better thinking I'd put an rcd on it.

I had assumed the need for an RCD went without saying. But either way it is pretty much irrelevant to the question of either a 3036 can provide overcurrent and fault protection.
 
I think the old definition of the protection offered by rewireable fuses was 'coarse' , that sums it up for me, and they're too easy to tamper with by those who shouldn't too. :yesnod:
 

Reply to electric shower change over in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

  • Question
Ok, thanks Dave.
Replies
2
Views
981
It's not uncommon to find the earth cable put out from the additional neutral knockout, not the designed one on the side. If the rest of it looks...
Replies
2
Views
856
  • Question
Any metalwork connected to the MET could rise in voltage compared to true earth under an open supply neutral fault (on TN-C-S), and that would...
Replies
24
Views
1K
Question 1 do you prefer buttered, salted or sweet salted? I'm guessing salty 😜 1. Auto range multimeter (used on mains before when testing the...
Replies
2
Views
489
  • Question
Thanks for letting us know. I think you made the right choice to be honest.
2
Replies
34
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks