Electric shower question

I'm not going to but let's say a house has no shower fitted at all in a domestic household and I wanted to fit one. If you have say sockets and lighting on a 40a breaker, and I wanted to FiT a 8.5kw shower from scratch, would u have to fit another 40a breaker separately for the shower, or would you fit it to the existing 40a breaker with the sockets and lighting? Just a question
 
Last edited:
Lots of things to take into account Lee, installation method, length of run any roof or wall insulation involved in the run etc.Why do you have lighting and sockets on a 40A breaker???
 
I no mate I am just saying for example I no you wouldn't have 40a you would have 32 and I no all installation method, just wondered would u take the shower off its only breaker if you no what I mean
 
a shower must be on it's own MCB. the rating to suit the cable size, which itself is determined by load, installation method, and volt drop calcs.
 