I hava a 185sqmm SWA/XLPE underground cable supplying 240kW(Peak) at 400v. Ambient temp. around 28 c .
  • What is considered the upper temperature limit the cable can heat upto?
  • What is the standard (theoretical calculation) available to get the overheating limit?
 
Hi - you can ask manufacturer to confirm, but max conductor temperature of 90 C may be possible, depending on the installation terminations also being rated to that temperature. Otherwise I use 70 C.
Is 28 C the ambient temperature of the air or the ground?
 
How much current are you pulling through that cable out of interest?


As already said, 90C for Thermosetting cable but terminations will likely only be rated for 70C. Where your terminations are will be subject to different rating factors though. E.g. you could have cable in buried ductwork in excess of 70C and termination points above ground at less than 70C which would be fine. Also, how deep is it buried and is it grouped with any other cables?
 
Sounds like a college question - not sure if he’d ask on a forum relating to a 185mm, that’s a big booger.
 

Reply to Electrical cable Overheating in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
811
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...
Replies
12
Views
1K
  • Question
If your using 35mm or 50mm use 2 core SWA and use the armour as the earth, it'll cut down on price. I know people will comment on this but the...
Replies
10
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top