Hi all, I am studying for a HNC in Building Services and have been set an electrical design question. I need to calculate the total load for a small factory, taking into account power factor, and diversity. I then need to select a back up power system bassed on my calculation.

Is the calculation i have done correct?

Loads

4 x 45 Amp CNC Machines = 180 Amps
4 x 32 Amp Conventional = 128 Amps
1 x 32 Amp Welding set = 32 Amps

No diversity has been applied.
180 + 128+ 32 = 390 Amps

390 Amps – Machining Load
42.8 Bench equipment & lighting Load
69.4 Amps Total Office Load

Total Ampage = 503 Amps

503 x 0.692 = 349.9kVA (Apparent power)

Taking into account 0.8 power factor
349.9 x 0.8 = 279 KW (Actual power)

I have determined 0.692 from calculating the below formula

Line Voltage of supply, which in this case in 400v
503 x (400 x 3) = 349.9kVA
1000

Have I calculated Kva correctly? Have I included power factor correctly?

Any feed back on this would be really appreciated.
 
Last edited by a moderator:
i would say yes mate, using the formula for Power in three phase P=SQRT3xVxAxPF gives about 279Kw, your actual power calculation, divide by 0.8 brings you back to 349kVA, so you sound right, thats not to say someone won't be along to correct me:nono:
 

Reply to Electrical Design in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
857
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
990

Similar threads

He needs to first be able to confirm the design current (Ib)
Replies
6
Views
999
I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
352

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top