Hi everyone.
There is something that confuses me so I hope someone could answer.
There is an electrical Hob which is 7.8KW and electrical oven which is lets say manufacture instruction says 13A so somwhere around 2.0KWs.
If you apply diversity on Hob it comes to somwhere around 17A and I know usually you use 32A MCB with 6mm cable to make it future proof.
Now Oven as its 13A many people yet wire it in a ring but what confuses me if you wire Oven with same MCB as Hob in the dual connection cooker unit then as oven is has a design current of 13A which is less than Nomimal current of 32A MCB but Iz for the oven is 2.5mm which can take around 20A so this makes IZ less than In which should not be the case.
I know as Oven does not overload so this is fine but in a faulty condition if Oven is wired in the same connection unit as Hob as Hob is 6mm it should be ok for the Hob but Oven with 2.5mm wouldnt it burn if fault occurs?
There is something that confuses me so I hope someone could answer.
There is an electrical Hob which is 7.8KW and electrical oven which is lets say manufacture instruction says 13A so somwhere around 2.0KWs.
If you apply diversity on Hob it comes to somwhere around 17A and I know usually you use 32A MCB with 6mm cable to make it future proof.
Now Oven as its 13A many people yet wire it in a ring but what confuses me if you wire Oven with same MCB as Hob in the dual connection cooker unit then as oven is has a design current of 13A which is less than Nomimal current of 32A MCB but Iz for the oven is 2.5mm which can take around 20A so this makes IZ less than In which should not be the case.
I know as Oven does not overload so this is fine but in a faulty condition if Oven is wired in the same connection unit as Hob as Hob is 6mm it should be ok for the Hob but Oven with 2.5mm wouldnt it burn if fault occurs?