Hi Guys just been asked to carry out an inspection at a warehouse. Got there and first two boards I saw were the really ones with rewirable fuses asbestos flash tape and exposed bus bars. There are a couple of new boards as well My question is should I just carry out a visual and fail it straight away or should I do a full inspection and fail it?
 
I guess you are doing an EICR. Your job is to carry out an inspection and comment on departures from BS7671.
See anything in the good book about asbestos?
So you cannot fail it on that basis.

You should make a comment about this in the notes section, perhaps with a replacment recommendation, but it cannot be a fail.

> You may need to think about your personal protection during the inspection process, though.
 
And am right in saying that the old boards do not meet any fire regs and that rewirable fuses are an automatic C2 nowadays
If the enclosure doesn't meet today's edition of the regs then its a C3, nothing more.
Rewireable fuses are perfectly acceptable, assuming EFLI etc allow their use.
 
“Automatic C2”....where’d you get that?. Recommend changing to cartridge fuses if you can get suitable carriers. You might have a point with the open busbars, though.
 
An EICR does not fail it is either satisfactory or unsatisfactory. BS3036 semi enclosed fuses are still in compliance with BS7671 but apply the correction factor for such devices when assessing overcurrent compliance, this should be rudimentary knowledge for a person carrying out EICRs. The presence of asbestos is a separate issue from BS7671 and you must follow your company policy when confronted with it.
 
I was under the impression that hse guide lines were to not disturb the asbestos so would not be able to remove the fuses safely.

You can safely work with asbestos in certain limited situations if you have some basic training. Here is a link to the guide you can purchase from the HSE.
Asbestos Essentials, HSG210: A Task Manual for Building, Maintenance and Allied Trades on Non-licensed Asbestos Work, HSG210 - https://books.hse.gov.uk/bookstore.asp?ACTION=BOOK&PRODUCTID=9780717665037

I highly recommend it as a very useful guide to understanding what you can and can't do and what to expect if you come across asbestos.

I did the non licensed full asbestos awareness course which allows me to work on non licensed asbestos removal and repairs. I highly recommend you look into this course. I imagine most local training providers will advise you on this.

Here is an example of one
Cat B Asbestos Awareness Training | Asbestos Training LTD - https://www.asbestostraininglimited.com/non-licensable-works-training/ukata-cat-b-training?gclid=CjwKCAiA5qTfBRAoEiwAwQy-6SV5T1FNyFRiabC16dQ5S5surKGshg1o8vxhAeN-uYtUnGoyAnj0AxoCWDAQAvD_BwE

It cost me around ÂŁ150 for a full day's course. It opened my eyes especially the fact that there are 6 main types of asbestos that are commonly put into 3 categories. Although asbestos is hazardous in general some types can be extremely harmful, especially if disturbed.
 
carry out a full inspection and list all defects, otherwise could be in a situation where customer agrees to pay to rectify first defect found, then you go back and find other defects, which means another conversation.
 

Reply to Electrical inspection and old boards with asbestos in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
947
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
There is no homework, and I'll never see these photo again.
Replies
3
Views
618
I usually put something like this To assess compliance with BS7671 for continued safe operation (5 year periodical inspection)
Replies
8
Views
454

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top