Electrical Installation Certificate - Supply Protective Device Characteristics | on ElectriciansForums

Discuss Electrical Installation Certificate - Supply Protective Device Characteristics in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Joined
May 7, 2012
Messages
117
Reaction score
24
What course of action is recommended when the type and size of supply protective device characteristics cannot be identified without pulling the fuse. I phoned the DNO and asked them for the info. Initially they told me to pull the fuse but later agreed that if I wanted that info they would send someone out.

In practical terms is it ever satisfactory to annotate this field as "not verified"?
 
Either that or you could put it down as a limitation. Although as you say not verified sounds better as at least you have made a effort to obtain it.
 
Speak to the client before hand and outline the limitations on the testing, then you can put this in the agreed limitations box along with say bridging out L+N to carry out IR tests.
 

Reply to Electrical Installation Certificate - Supply Protective Device Characteristics in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
295
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
804
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
839

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
487
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
996

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top