LmarshallSparks
Supporter
Hello All,
I have a slightly different question today, I have a customer who has multiple lights without CPCs terminated, the cables completely lack a CPC, however in some rooms they have a CPC and in other rooms they do not, so yes a CPC leaves the board, but does not run to all light fixtures and switches! Most of the class 1 equipment has a CPC, however the class 2 equipment rarely does!
The customer has the entire house wall papered in a beautiful finish with a discounted wall paper! Simply put they do not want a rewire at all!
I would like to suggest that we replace all the switch’s for modern versions with the white rubber caps covering the screw heads - Regulation 410.3.9 (iii) - To my knowledge this regulation states that the screws are small enough not to require earthing however the caps would offer increased protection!
I also believe that class 2 ceiling roses do not require an earth? Regulation 411.3.1.1
I would like to find a solution that avoids a rewire as the house is currently protected by 100mA RCD, I want to fit a new board with 30mA protection! But I obviously can’t fit a safer board if the circuits are not safe!
I have a slightly different question today, I have a customer who has multiple lights without CPCs terminated, the cables completely lack a CPC, however in some rooms they have a CPC and in other rooms they do not, so yes a CPC leaves the board, but does not run to all light fixtures and switches! Most of the class 1 equipment has a CPC, however the class 2 equipment rarely does!
The customer has the entire house wall papered in a beautiful finish with a discounted wall paper! Simply put they do not want a rewire at all!
I would like to suggest that we replace all the switch’s for modern versions with the white rubber caps covering the screw heads - Regulation 410.3.9 (iii) - To my knowledge this regulation states that the screws are small enough not to require earthing however the caps would offer increased protection!
I also believe that class 2 ceiling roses do not require an earth? Regulation 411.3.1.1
I would like to find a solution that avoids a rewire as the house is currently protected by 100mA RCD, I want to fit a new board with 30mA protection! But I obviously can’t fit a safer board if the circuits are not safe!