Hello everyone

i recently got a job on replacing a BMS panel in a plant room. the NEW panel i installed except the control side of the install also feeds the mains for a few gas boilers, immersion heaters and cylinders, pumps. etc. I am going to do the testing on that and i realised that some of the D.O.L circuits in the panel are is not fed from a MCB but are connected straight to the isolator that is fed from the main DB. meaning that the only for of protection on the D.O.L is the 50A mcb that feeds the panel.

now up to the D.O.L circuits the wirings is done with 10mm singles and on the outgoing side with lower rating cores depending the rating.

is that acceptable and if how do i record the DOL on my EICR?

i am New to testing as well so i don't have a lot of experience specially when it comes on BMS panels
 
Are you certain these circuits are connected directly, have you missed anything?
I've worked on hundreds of BMS panels and never seen any circuit without suitable protection.
 
Are you certain these circuits are connected directly, have you missed anything?
I've worked on hundreds of BMS panels and never seen any circuit without suitable protection.
Yes most positive. i physically traced the cables going to the main isolator, and i also have it on the drawings. thats the picture of it and basically is as shown on the drawings[ElectriciansForums.net] Electrical test on D.O.L fed straight from main panel isolator
 
Last edited by a moderator:
Assuming these DOL starters include overload protection then I dont see any technical issue.
The 10mm singles should have adequate fault protection from the 50A MCB and overload protection is provided by the overloads on the DOL.
 
Assuming these DOL starters include overload protection then I dont see any technical issue.
The 10mm singles should have adequate fault protection from the 50A MCB and overload protection is provided by the overloads on the DOL.
Yes they do have overload protection.
Electrically i don't see something wrong aswell but then how do i record this on the test sheet where i usually have the type of the mcb rating etc get max ZS permitted and everything.
 
So I did a bit of research online and I found that the motor starter that is used is in accordance with iec 60947-4-1 . I will have to calculate the max zs through the equation from the info thats provided in the starter datasheet.
 
Yes they do have overload protection.
Electrically i don't see something wrong aswell but then how do i record this on the test sheet where i usually have the type of the mcb rating etc get max ZS permitted and everything.

Find out the max Zs and record each one as a new circuit.

Or else create your own record of test results that is better suited to the type of installation.
 
Find out the max Zs and record each one as a new circuit.

Or else create your own record of test results that is better suited to the type of installation.
Yeah that's what I did in the end. I got data sheet from the manufacturer and calculated the max Zs for each of them.
 

Reply to Electrical test on D.O.L fed straight from main panel isolator in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
766
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
774

Similar threads

Busbar chambers are often considered what's often termed as 'fault free zones' as per BS EN 61439 where firstly the primary purpose of protection...
Replies
2
Views
1K
In TN-S systems, you shouldn't isolate the neutral in a 4-pole isolator. Connecting neutrals to a dedicated terminal is acceptable and safe...
Replies
4
Views
635

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top